  • Jan 1, 2008, 09:27 PM
    homeadvice
    No heat and furnace not run at all.
    My heater does not come on and I don't hear the igntion click when I turn on the heater.
    The a/c and the fan works fine when turn on, but no heat. Silent.

    Could this be a faulty INTERMITTENT PILOT or a bad ignition moduel(circuit board).

    My furnace is equip with the electronic ignition device.

    Any inputs greatly appreciated and happy new year!
  • Jan 2, 2008, 12:55 AM
    hvac1000
    Brand and model of furnace?
  • Jan 2, 2008, 02:31 AM
    homeadvice
    Thanks for your inputs.
    The furnace is goodman manufacturing corp. forced air furnace with electronic ignition. Don't know the model. Its more than 15 years old.

    Intermittent pilot from united technology HSC electronics.
    Non-100% shutoff
    Ansi z21-120 1985
    24 vac 60hz 150ma.
  • Jan 2, 2008, 07:18 AM
    hvac1000
    Since the heat is dead I suggest you trace the wiring through the heat circuit before replacing parts and also check for a good ground on the United Technology spark box (the gray box on the right side).
    If I were to take a guess at the defective part causing this I would first suspect the United technology spark box. You might also want to clean or replace the flame sensor.

    Make sure to check for voltage passing through the fan safety control located on the left upper part of the front. If no voltage there it will not allow the spark box to activate. Also many of these units were shipped with a white porcelain safety control also visible on the front of the burner area just up from the burners. That can also open and stop the control voltage from activating the unit.

    Note if the porcelain safety proves defective you might want to check for a obstruction in the flue area since it is a roll out type of safety device.

    One last note the numbers you posted for the furnace model are not correct. Those are the numbers from the spark box.
  • Jan 2, 2008, 12:33 PM
    homeadvice
    Thank you hvac1000, goodman furnace, model no. gux 060-3 rev s

    Serial no. 8902000 25

    Input 60,0000 btu/hr.

    I hope this will give you a better view to my heating problem.

    Thank you so much.