Heat pump reaches setpoint but won't turn off
Hi...
I have a Janitrol heat pump (I don't know the model number) controlled by a Robertshaw thermostat (model #9520).
I am having a problem with the heat pump warming the house to the normal setpoint for comfort (say, 70 or 71) during the day but the heat pump continuing to run. By continuing to run, I mean the whole system, inside and outside units (fan, compressor unit).
Today, we are having temps in the mid- to upper-40s. I had I lowered the setpoint to 66 and the unit would turn itself off. However, if I raise the setpoint, the problem with it continuing to run recurs.
On especially cold nights (in the 30s or even into the high 20s), the heat pump will run for hours without cutting off and it doesn't appear that the auxiliary heat ever comes on.
I called an HVAC service to come out Monday (Christmas Eve) and the tech looked things over. He said the refrigerant level, compressor, defroster, heat strips, etc. all seemed fine. He pressed the reset switch on the thermostat and said that might clear it up. If not, he said I may need a new thermostat.
He explained how auxiliary heat worked and said that if it's cold enough outside for the heat pump to not warm house sufficiently to shut the system off, the auxiliary heat should kick in to help to reach the setpoint. (He also said that if the heat pump warmed the house to setpoint, but the unit continued to run for a lengthy time, the auxiliary heat should come on long enough to help the unit shut off.)
Today's example, as I type: I had the setpoint at 66 since this morning. While reading over this site, I reset the thermostat to 69. The unit has raised the temp to 69, but now the heat pump is continuing to run and there is no sign of the auxiliary heat coming on, although the setpoint of 69 was reached 15 minutes or so ago.
It sounds reasonable to me that this may be a thermostat issue, but I wanted to see if I could find any other information/assistance that might help confirm that diagnosis before I purchase a new thermostat.
The tech also advised that if I go with a new thermostat, to stay away from Hunter and preferably go with a Honeywell. Your thoughts on that would be appreciated as well.
Thanks!
--Paul
UPDATE: about 25-30 minutes after reaching the setpoint of 70 this afternoon, the unit just shut off.