My question is, how do I take a line that is wired to both terminals of a double 20 amp breaker and make it so I can use it as a normal 110 volts service for a switch. To start I found that a meter reading of 110 volts was achieved by putting the terminals on either the black or white wire and the ground. After talking to an electrition at work I was advised to take the white wire out of the 20 amp breaker and place it on the neutral bar, did not work- no power at receptacle. Then I tried adding the black to an existing 15 amp breaker, still nothing, so I then took the black wire from that 15 amp breaker and put it in the 20 amp breaker and that fixture worked. I then put the original black wire in 20 amp breaker and still nothing happened. So what do I do, is the problem the wire gauge?