4 wire stat controlling two devices?
I've set up a 240V heater in my garage but due to space restrictions it's mounted on a shelf about 7' above the floor. To keep the air circulating I've added a shroud to the intake of the heater with a 6" round duct to the floor for a cold air pick up.
The heater's element seems to be running too warm so I'd like to add an auxilary fan in the 6" duct to improve air flow while the heater is running.
Can I use a 4 wire stat to control the 240V heater with 2/4 wires and a 120v fan in the duct with the other 2/4 wires? I believe the stat is a double pole unit, something I will double check with my volt meter, meaning it basically has two circuits/switches that are opened & closed by a single relay. It's a Honeywell stat #CT410B
Please confirm or correct me :)
Thank you.