Goodman GMP100-3 Furnace Won't Stay On.
Hello,
I have a Goodman Furnace (model # GMP100-3). The furnace will not stay running. Here is the sequence of events for two different scenarios that are occurring.
Scenario 1
1. Thermostat Calls for Heat
2. Inducer starts
3. Pressure switch closes
4. Heating element glows
5. Burners Ignite (flames nice and blue, everything looks good)
6. Blower Comes on, House Starts warming up, but stops well before temperature is reached. There is no set amount of time for this (sometimes 10 seconds, sometimes 5 minutes)
7. Burners extinguish prematurely and blower continues to run.
Scenario 2
1. Thermostat Calls for Heat
2. Inducer starts
3. Pressure switch closes
4. Heating element glows
5. Burners Ignite and immediately go out. Just a flash of flame is seen with no rollout
Other info - For scenario 1, the diagnostic LED flashes three times which means "pressure switch failure to close" and to check venter, pressure switch, vent blockage. I got a new pressure switch and changed it out (no improvement). I pulled off the flue pipe and checked for blockage and it is clear. I checked the hose running from the inducer to the pressure switch, and it is in good condition. I have also cleaned the flame sensor.
I guess here are the questions - Is it possible for blockage further up the chimney to cause this? Could it be a bad inducer not keeping the new pressure switch closed? I also checked the opening in the inducer. I put in a small drill bit and it goes in freely for the first inch, then hits something solid, is this normal? Should I force the drill bit in further?
Right now, given the two different scenarios, could this be a faulty gas valve as the burners just extinguish at different times? What else should I check
Apologies for a lengthy post, but I wanted to try to give all the info.
Thanks in advance for your help,
Mike