  • Dec 14, 2007, 07:08 AM
    akalikar
    Tripping of ac mcb on dc current below its rated current
    Please let me know why ?

    MCB rated for 240/415VAC, 6Amperes trips on 5 Amps DC current at 24VDC voltage level

    Ambient operating temperature: 32 ° C
    MCB Designed for ambient temperature of 55° C


    Why MCB should trip:confused: ?
  • Dec 15, 2007, 09:31 AM
    tkrussell
    Very possible that a loose connection, while the current is low, still, a loose connection will create a high resistance that can create heat at the connection, If this connection is at or near the breaker, the heat created will be conducted through the wire or components of the breaker and migrate into the breaker and activate the thermal component in the breaker,causing a trip.

    The breaker must be rated to handle DC, also.
  • Dec 15, 2007, 10:33 AM
    Tj3
    Let me add that you also did not say if the breaker was new, or how old the breaker was. As breakers age, they trip more easily and at lower currents.