Ask Me Help Desk

Ask Me Help Desk (https://www.askmehelpdesk.com/forum.php)
-   Heating & Air Conditioning (https://www.askmehelpdesk.com/forumdisplay.php?f=150)
-   -   Faulty limit switch? (https://www.askmehelpdesk.com/showthread.php?t=16207)

  • Dec 18, 2005, 02:27 PM
    snigadnol
    Faulty limit switch?
    Toward the end of a heating cycle, the burners would shut down and the fail code would read "open limit switch". The repairman said the limit switch was faulty and installed a new one a couple of days ago. It seemed to work fine until this morning, and now it's doing the same thing as mentioned above. What's up?
  • Dec 18, 2005, 03:32 PM
    wheatnbarley24
    You need to make sure your filter and cooling coils are both clean. You also need to check your vent pipe for any obstruction
  • Dec 18, 2005, 05:48 PM
    labman
    The control board could be going bad.
  • Dec 20, 2005, 08:33 PM
    snigadnol
    Faulty Limit Switch
    Thanks for all the advice. Here's an update:

    I had the servicemen back in to investigate. The cooling coil was clean. The limit switch was working properly. The vent seemed clear. Then we tried running the furnace w/o a filter in, and the limit didn't open - everything seemed to work just fine. The service guys think that probably the return ducts are just adequate to provide the needed air for the plenum. I had a higher quality air filter, but this also reduced the volume of air that could be pulled into the plenum, so things would get too hot. They suggested I use a cheaper, lower quality filter and just change them more often. The other solution would probably be to add more return ductwork to feed the furnace.

    So the furnace is working, but does anyone out there have any other suggestions so that I might be able to use a better filter?
  • Dec 20, 2005, 10:09 PM
    labman
    Usually the blowers have several speeds available selectable by changing jumpers on the control board. If the air flow is marginal, the furnace may not be operating as efficiently as it should. You will need the schematic for the furnace and some time to figure out changing the jumpers yourself. You might talk to the technicians too. Perhaps if it was as simple as that, they would have done it. May need a bigger motor.

    Could look into an electrostatic filter, no restriction and very efficient filtering.
  • Dec 21, 2005, 03:44 PM
    wheatnbarley24
    What size is your return air? What size unit do you have?
  • Dec 21, 2005, 05:11 PM
    caibuadday
    [QUOTE=wheatnbarley24]What size is your return air? What size unit do you have?[/QUOTE... you could expand the surface area of the filter (reduce obstruction) by install "V" shape filter rack... *** instead of single filter; V filter rack use 2 or more filters...