Quote:
Originally Posted by tkrussell
Before I continue with any advice, I need to know the horsepower of the pump. That is what will determine the size of the breaker.
I went back to the other post and found the pump is 115 volts 1/2 HP.
This needs a single pole 20 amp circuit breaker.
That is correct, it is 115 volts 1/2 HP
Quote:
Am I following this correctly, one, a 120 volt pump was fed with 240 volts, and it kept running or did not do any damage?
The first pump it took almost 2 months hooked up wrong, before it died. That is not to say that there wasn't damage, only that the previous pump went 2 months before it finally burnt out.
Quote:
And now, to change the feed to 120 volts, a wire was connected to ground?
I could be descibing this wrong. The conduit had 1 black wire, 1 white wire, and ground. The plumber took the white wire and connected it somewhere else, I assumed it was ground. He said this would complete the circuit so that it was only sending 120 volts. Pump has worked correcly since this was done.
Quote:
I am curious how this is connected to "ground". Did you only use one of the two 240 volt hot legs, and connect the neutral return from the pump to the bare equipment ground wire? If so, this is still not wired properly.
Yes, there is only one hot leg going to the pump now. Plumber said that it wasn't wired right, but would allow the pump to work correctly with the correct voltage until we rewired it correct, or until we got the correct pump.
Quote:
And, someone has to say it, may as well be me, it took a plumber to figure out the voltage rating of the pump was different that the supply voltage, and not the electrical engineer?
Lol. In the electrical engineers defense, he was on the phone, and not actually here. The plumber actually had eyes on the system.
Quote:
I assume the word "watts" was in error and meant to mean volts?
Yes, your assumption is correct.