  • Dec 1, 2007, 05:17 PM
    szworrior
    Electrical wiring for lights
    Can I use 240v wiring in 120v system for lights?

    Thanks
  • Dec 1, 2007, 05:21 PM
    Stratmando
    Wire that is good for 240 volts is good for 120. Do you mean 240 volt bulbs, or 2 120 volt bulbs in series?
  • Dec 1, 2007, 05:22 PM
    tkrussell
    The rating of wiring can meet or exceed the rating of the devices on the circuit, just the voltage cannot exceed the voltage rating of the devices.
  • Dec 1, 2007, 07:52 PM
    labman
    Isn't most of the common stuff such as NM-B, THHN, etc. all rated for 300 volts?
  • Dec 2, 2007, 05:43 AM
    Cobraguy
    Just to make sure... you aren't talking about an existing 240V circuit that you are trying to convert to a 120V circuit are you? That's an entirely different animal. It can be done, but requires some work in the panel.
  • Dec 2, 2007, 06:15 AM
    tkrussell
    The standard wiring is rated for 600 volts.