Ask Me Help Desk

Ask Me Help Desk (https://www.askmehelpdesk.com/forum.php)
-   Heating & Air Conditioning (https://www.askmehelpdesk.com/forumdisplay.php?f=150)
-   -   Furnace can not start (https://www.askmehelpdesk.com/showthread.php?t=158102)

  • Dec 1, 2007, 02:31 PM
    ec2000
    Furnace can not start
    I have a Frigidaire FG6RK072C-12 furnace for about 7 years. It started to have problems a couple days ago. The motor was running and then ignitor was on. But the burner might on for a short period and then cut off or it would start and cut off right away. I got a "pressure switch stuck closed" indication. Even I changed a new pressure switch, I still had the same problem. The system seamed quite sensitive, I just touched any wire, it started a new cycle again. Note that I did try to make sure all connections are properly connected. Could this likely be the control board problems or I should open up the motor to do some clean up/rubrication?
  • Dec 1, 2007, 06:03 PM
    hvac1000
    If you touch any wire and it does that the first thing I would check is for a bad or corroded ground connection. Check and report back. The ground wire is supposed to be green but can be any color. Loosen wire then retighten.
  • Dec 2, 2007, 11:20 AM
    ec2000
    Thank you hvac1000! Your suggestion was quite good since it triggered me to review all connections of furnace one more time. The ground wire connection was fine. I used a volt-meter to make sure the ~0 ohm. After turned on the power, I touched the white wire from thermostat and ground. I did get ~26ACV and you know what the furnace was running as normal until I took out the measurement. I tried this twice and got the same behavior. So I checked the wires from the thermostat t the control unit. I found the yellow wire a little bit loose so I secure it. It runs now and hopefully it will stay this way.
  • Dec 2, 2007, 11:25 AM
    hvac1000
    Good deal glad you got it fixed.