    Goodman furnace .code 3
    :confused: New unit... less than 1 year old... won't start on heat... throws code 3??
  • Nov 23, 2007, 08:09 AM
    acetc
    Look on the furnace panel for this code, it will tell you what this code 3 is .
  • Nov 23, 2007, 08:55 AM
    Dan Habluetzel
    Quote:

    Originally Posted by acetc
    Look on the furnace panel for this code, it will tell you what this code 3 is .

    Dan here... Serviceman that did install says it is probably the small fan that clears the fumes from box NOT starting (it didn't... just a hummm from the entire unit)... the code is described as "pressure switch stuck open"... he says sometimes just a nudge of the squirrel cage will set it free and be good to go... we'll see... he is checking it now... Dan H.

    Addendum... that was it... easy fix... just gave the old squirrel cage a VERY slight nudge... operation is RESTORED... no parts required... hope this helps others... Dan Habluetzel.