Originally Posted by tkrussell
I am assuming the ferenfite is a typo for the actual brand name of "Fahrenheit", which is marketed by Lowe's.
Each of these heaters are 2500 watts, and at 240 volts each draws 10.41 amps.
The maximum current allowed on a 20 amp 240 volt heating circuit is 16 amps, so you cannot have more than one heater on a 20 amp circuit, let alone 3 or 4 units.
A 30 amp 240 volt heating circuit can have a max of 24 amps, so you can connect 2 of the 2500 watt heaters on one 30 amp circuit.
A 30 amp circuit will need all #10-2 cable.
You can either run each heater on it's own 20 amp circuit with the #12-2 cable, each with it's own thermostat, or run two 30 amp circuits with all #10-2 cable.
How would you like to proceed from here?
I assure you if you do connect all these 4 heaters on a 20 amp circuit, you will have serious problems, unless you don't mind seeing fire apparatus parked on your front lawn.