Goodman furnace ECM motor blowing too much air?
I installed a Goodman GMV95 two speed gas furnace with ECM fan motor last fall. It functioned perfectly last winter, cutting my natural gas bill almost in half. When I installed the unit, I set it for 720 cfm (my ductwork is a little small for 95% efficient equipment) and verified the airflow by clocking the gas meter and checking temperature rise. My static pressure was under .3 inches on high fire.
Two months ago I started it up and notice a lot of blower noise and low temperature rise. The static was running 0.7", and I used a Tru-flow plate to find the airflow was a little over 1000 cfm. The green LED that is supposed to flash airflow wouldn't work, it just flickered dimly. Otherwise, the unit is running fine.
So far:
1. Checked all the ductwork, the electrical ground, thermostat connections, cleaned HTX.
2. Replaced control board - nothing. I switched to a spun glass filter to get the static down to 0.5" - in the range that Goodman requires when firing.
3. Called Goodman tech support.
4. Cleaned all connections, checked for moisture.
5. Called tech support again, changed the endbell (control module) on the ECM motor.
The static is still at 0.5", and I think the airflow is still high. The green LED is working now, and flashes 7 times (700 cfm). I will bring the Tru-flow plate home next week to check airflow, but I may repeat the temp. rise / meter clock to verify the airflow this weekend.
Has anyone had an ECM motor that just doesn't seem to blow the correct amount of air for what it's programed?:confused:
P.S. - I don't have an AC coil on the unit yet.
Comment on hvac1000's post
The tech guide is very good - now I know what else to check!