  • Nov 8, 2007, 08:27 AM
    tholdswo
    Lights go off after 30 minutes
    I have two ceiling lights on the same circuit in my bathroom. After 30 minutes of being on both lights go off. If I do nothing one light will come back on after a random interval of time. If after going off and I turn the lights off at the switch the lights will work again after waiting 30 minutes. Any help?
  • Nov 8, 2007, 10:16 AM
    ebaines
    Sounds like these lights have a thermal overload switch that is kicking in. If the fixture gets too hot it automatically turns itself off, so as to avoid becoming a fire hazard. Are these ceiling lights the recessed can type? Many (maybe all?) recessed ceiling fixtures have this feature. If these are in a ceiling that has insulation (such as in a ceiling directly below the attic), perhaps the insulation is stuffed too tightly around the recessed can, causing the heat build up.
  • Nov 8, 2007, 11:11 AM
    KISS
    Another reason is exceeding the maximum wattage lamp that the fixture will accommodate.
  • Nov 8, 2007, 12:16 PM
    tholdswo
    Comment on ebaines's post
    Thank you. These are can lights in the ceiling below the attic. I will check the insulation around the light.
  • Nov 8, 2007, 12:18 PM
    tholdswo
    Comment on KISS's post
    Thanks. Bulbs are 60 watt and hopefully not overloading.
  • Nov 8, 2007, 02:59 PM
    KISS
    It's not amps, but the heat generated from the lamps. Look for a max wattage on the fixture. Try substituting 40 W lamps temporarily. I agree with the ventilation/isulation as well.
  • Nov 9, 2007, 12:41 PM
    tkrussell
    Many times it is the type of bulb and not the wattage of a lamp that causes this heat.

    Example, a recess fixture that is rated for an 100 watt R- Reflector lamp, has a standard 60 watt A lamp in it. The reflector lamp is designed not only to push out the light but heat also, and the fixture can handle 100 watts. But us a standard A lamp, which is your typical household incandescent lamp, does not have the benefit of the reflector.

    The lower amount of heat from a 60 watt lamp becomes entrapped in the fixture that wants a reflector lamp, and causes the thermal cutout to trip.

    So, along with checking if any insulation is covering the fixture, be sure to use the proper lamp in the fixture.