  • Nov 9, 2005, 12:19 AM
    mbeychok
    Cooling tower evaporation, blowdown, makeup and cycles
    Here are the governing relationships for the makeup flow rate, the evaporation and windage losses, the draw-off rate, and the concentration cycles in an evaporative cooling tower system:

    http://www.air-dispersion.com/CoolingTower.gif

    M = Make-up water in gal/min
    C = Circulating water in gal/min
    D = Draw-off water in gal/min
    E = Evaporated water in gal/min
    W = Windage loss of water in gal/min
    X = Concentration in ppmw (of any completely soluble salts … usually chlorides)
    XM = Concentration of chlorides in make-up water (M), in ppmw
    XC = Concentration of chlorides in circulating water (C), in ppmw
    Cycles = Cycles of concentration = XC / XM
    ppmw = parts per million by weight

    A water balance around the entire system is:

    M = E + D + W

    Since the evaporated water (E) has no salts, a chloride balance around the system is:

    M (XM) = D (XC) + W (XC) = XC (D + W)

    and, therefore:

    XC / XM = Cycles = M / (D + W) = M / (M – E) = 1 + {E / (D + W)}

    From a simplified heat balance around the cooling tower:

    (E) = (C) (ΔT) (cp) / HV

    where:
    HV = latent heat of vaporization of water = ca. 1,000 Btu/pound
    ΔT = temperature difference from tower top to tower bottom, in °F
    cp = specific heat of water = 1 Btu/pound/°F

    Windage losses (W), in the absence of manufacturer's data, may be assumed to be:

    W = 0.3 to 1.0 percent of C for a natural draft cooling tower
    W = 0.1 to 0.3 percent of C for an induced draft cooling tower
    W = about 0.01 percent of C if the cooling tower has windage drift eliminators

    Concentration cycles in petroleum refinery cooling towers usually range from 3 to 7. In some large power plants, the cooling tower concentration cycles may be much higher.

    (Note: Draw-off and blowdown are synonymous. Windage and drift are also synonymous.)