  • Oct 28, 2007, 05:28 AM
    GrayWolf45
    Intertherm furnace
    Hi I have a Intertherm Model MMHA 070ABHr-01 gas. Had a tech out replaced the ignitor/and adjusted it. Problem still is furnace calls for heat prepurge fan motor kicks?? In, ignites runs for 2-3 minutes kicks out fan motor starts runs for 30 sec shuts off. In the mean time the furnace has restarted only this time it will finish the whole heating cycle.?
  • Oct 28, 2007, 11:32 AM
    hvac1000
    Try setting the thermostat higher to see if that helps. If not post back.
  • Oct 29, 2007, 04:12 AM
    GrayWolf45
    Ok that seems to work ,but I can`t keep setting it higher each time. Bad thermostat?
  • Oct 29, 2007, 04:19 AM
    hvac1000
    You might have to adjust your thermostats heat anticipator. Look in the sticky notes at the beginning of this board for info.
  • Oct 29, 2007, 06:51 AM
    GrayWolf45
    Ok I`ve the ajusted anticipator it to short cycles ,seems to work the best but furnace runs every 15 minutes. Larger cycles seem to produce the same problem as first stated. Programmable thermostat the answer? Lower temp to kick in higher temp to shut off/. Seems if a manually set the temp higher 4-5 degrees it runs perfect.
  • Oct 29, 2007, 12:12 PM
    hvac1000
    Yep sounds like a thermostat or thermostat location problem.
  • Oct 29, 2007, 06:09 PM
    juggallojed
    Do this before replacing the t-stat,( I've had 8 spiders nest in 3 days)this is the same situation
    Measure the air in and air out,, if you temperature difference is too low ,you may have a small flame, this will cause the fan to short cycle. Possibly a spiders web in the gas orifice?

    Again, just a guess