-   -   Noma thermostat 52-2558-8 can't turn on hear (https://www.askmehelpdesk.com/showthread.php?t=144406)

  • Oct 24, 2007, 10:22 AM
    HONESTMAN
    Noma thermostat 52-2558-8 can't turn on hear
    Noma 52-2558-8 programmable thermostat

    --------------------------------------------------------------------------------

    I have just installed this new thermostat to replace an old non programmable one.
    I have a gas furnace, no air conditioning, my old thermostat have five wires
    Red, Green ,black ,white and orange.
    I connect wire:

    RH(red)connected to RH terminal

    RC(black)connected to RC terminal

    Y(orange)connected to Y terminal

    G(green) Connected to G terminal fan relay

    W(white) Connected to W terminal heating relay

    And remove the jumper between the RC and RH terminal on the thermostat.
    When I set temperature low than current temperature Heat will not come on(old thermostat heat and fan will turn on at same time) but the heat symbol on the thermostat is flashing, when I switch fan from AUTO to ON, fan began work, but heat still doesn't work.
    I also checked furnace power turn on.

    Anybody can give me advice?


    Thanks a lot
  • Oct 24, 2007, 04:27 PM
    hvac1000
    Read the sticky notes at the beginning of this board. Many times the color code was changed by the original installer. You will have to trace the colors back to see exactly where they go on the furnace. Just for a interesting experiment reverse the RH and RC wires. This will switch the 24 volt legs of the transformers. That might just do the trick.
  • Oct 24, 2007, 07:21 PM
    labman
    Go to the furnace and note which wires are connected to R and W. Connect the same wires to RH and W. Swapping the black and red will only work if the black is connected to R at the furnace.
  • Oct 25, 2007, 11:56 AM
    HONESTMAN
    I went to the furnace and found 5 wires are connected to 4 terminals "W"(white wire), "G"(green wire), "Y"(orange wire), "H"(red wire)and that red wire with a black wire jonin toghter turn to 2 wires(red wire and black wire) go to thermostat.
    I just want to know black wire(RC)connect to terminal "RC" and red wire(RH) connect to terminal "RH" is right or not.
    Do I need to insert the jumper between terminal "RH" and"RH" on thermostat?

    Thanks a lot
  • Nov 2, 2007, 04:27 PM
    rajukakkar
    I will strongly suggest to contact the company manufacturing NOMA. They have got an excellent customer service. I had good experience with my issue.
    It is better if you can send a mail diectly to them with your problem & they will certainly reply.

    Mail - [email protected]
    Company - UPM Marketing Inc.
    UPM Marketing Inc. - UPM
    Calgary AB Canada
    Fax 1 403 294 0881
    Toll Free# 1-888-468-6876

    :)
  • Nov 4, 2007, 06:09 AM
    HONESTMAN
    Thanks your advice. I have solved my problem.




    Honestman