I am installing a 30 amp 250 vac unit unit. The distance from the panel box to the plug will be approximately 110'. I am planning on using 12g wire. Will this suffice or should I use 10g?
![]() |
I am installing a 30 amp 250 vac unit unit. The distance from the panel box to the plug will be approximately 110'. I am planning on using 12g wire. Will this suffice or should I use 10g?
#12 wire is only rated 20 amps.
A 30 amp circuit needs a minimum of #10 wire.