  • Sep 23, 2007, 08:37 PM
    TexasMom2
    Wiring new range/oven to smaller wires
    We have an old wall oven and cook top, circa 1950's in our home. I want to know, is it okay to wire my new freestanding oven/range using 8/3 wire to the existing 10/3 wiring in the wall on the existing 40 amp breaker. Will it trip the breaker if I cook using the oven and the range or will it melt the wires and cause a fire? How safe is it and is it recommended. :confused:
  • Sep 24, 2007, 04:06 AM
    tkrussell
    A 40 amp circuit needs a minimum of #8 wire, or the risk is overheating of the #10 wire, and risk of fire.

    Usually a cooktop/oven combination uses a #8 feeder cable that junctions to two #10 cables for each of the appliances at one of the appliances.

    Are you sure the wire leaving the breaker is #10?