Isolating neutral bus bars
Ok, I picked up a Siemens main lug panel (convertible to main panel). Anyway, it has a grounding bar attached directly to the panel along one side. It also has 2 neutral bars on either side of where the breakers install and those are isolated from the panel by the plastic frame that holds all the components together. It looks like a main panel without the main breaker. Does my description of the ground and neutral bars make sense and is that what you were referring to?
There is a large green screw at the top of one of the neutral bars. A sticker in the box says to torque that screw to bond the neutral (I'm reciting from memory and don't recall exactly what it said). I'm thinking that I want to remove that screw and that it is only there if you were to convert the panel to a "main panel" in which case you would want the neutral bars to have a connection to the panel itself (bonded?). Is this correct?
Quote:
Originally Posted by tkrussell
The panel will come with a neutral bar, you will also need an equipment ground bar.This will bolt directly to the panel's backbox.The panel may come with one, if not you need to buy it separately.
All the branch circuit neutrals (white wires) will go the the neutral bar, which is insulated from the panel backbox. The panel may come with a green screw or a jumper wire. Do not use either. They are intended to bond the neutral bar only if the panel is a main panel.
Any green or bare wires coming back from the house circuits will need to go onto the equipment bar.
Hope this helps to claify. Get back if you have anymore questions.