How do I adjust the pressure regulator on a Pumptrol to increase the amount of pressure?
![]() |
How do I adjust the pressure regulator on a Pumptrol to increase the amount of pressure?
You will have a switch, probably near the pressure tank, which turns the pump on and off. This is where you will adjust the pressure upward. To quote Speedball, "I'm going to assume that you have a "square D pumptrol. First turnoff the power at the breaker box, then pull the cover off the pressure switch and you will see two spring loaded bolts secured with nylon nuts. One tall, one short. To increase the cut in pressure, turn the nut on the tall bolt down. To increase the cut out pressure,(that's the one that will give you more pressure) turn the nut on the short bolt down. This should give you the additional pressure you desire. "Quote:
Originally Posted by Vincent Montoya
Let me put up a image to help. SpeedballQuote:
Originally Posted by jlisenbe
Thanks for the picture. I've not been able to find it on the internet. It's always nice to have your answer as well. Whenever I adjust mine, the directions are inside the cover and I read them but that is not always available.
I found a lot of good info on this site, so maybe you all can answere my question, if the homeowner is getting air in her system once in a while, and they are on a well system, what could be the cause of that?
Your pump is likely pumping some air, probably due to the water table dropping during a dry summer. But before we go there, what kind of pressure tank do you have? Is it a galvanized tank, or a bladder type tank (probably blue)?
Please help the pressure is good but I don't know which way the L shape arm needs to be water will come on but when it kicks off it won't come back on
Not sure what you mean. Are you saying that the water runs for a while, then the pump will not kick back on?
That is exactly what I am having a problem with. I need to trip the little arm a few times on the pressure regulator switch to get the pump back on. When I trip the arm as a do it the pressure on the gauge goes up and then the pump kicks in?
30-50 pressure switch. Switch and tank have just been replaced. Should I check the pressure on the tank. Should it be 28 lbs. I haven't checked that yet.
What, exactly is your problem. Several problems were discussed here.Quote:
That is exactly what I am having a problem with.
Start a new thread and describe your problem. Every bodies problem is different.
8 times out of 10 when we flush the toilet the pump shuts down and doesn't kick back on until I do as described above. I have to manually trip the lever on the side of the pressure regulator a couple times until the pressure on my gauge comes up, then it catches and takes over the cycle by itself. Doesn't shut down using the sink or the shower just the toilet, so it probably has to do with the small amount of water being used to fill the toilet tank. Although when the shower runs you may get a blast when the pump cycles. Seems like the tank and pump may be out of sinc?
Pump not picking up at the right pressure?
1. Check the pressure at the top of the tank. For a 30/50 switch, it should be set to 28#. Do this with the power turned off and pressure drained to zero by opening up a low level faucet.
2. Where is the pump, above ground or in the well?
3. Why did you replace the old tank and switch?
4. When you replaced the switch, did you also replace the little pipe leading to the switch, or at least make sure the existing pipe was clean?
5. The little lever on the side is a safety measure. If the pressure drops to, in your case, 20#, then the switch "thinks" that the pump is running dry since pressure has gone so far below the 30# cut in point. The switch cuts the pump off at that point. When you pull the lever, you reset the switch.
All times are GMT -7. The time now is 02:01 AM. |