Honeywell Blank Thermostat
	
	
		I have a Honeywell T8011R thermostat.  It is blank.  I have 120 vac coming in, the transformer has 28 vac coming out.  The 5 amp fuse is fine and the control switch is on.  On the circuit board with the 5 amp fuse,  the brown wire from the transformer shows 28 vac, the double brown wire under it is 0 vac.  The red wire under that shows 28 vac.  The grey wire under that one shows 0 vac.  And the last red wire under that one reads 28 vac.  I think the circuit board may be the problem but I am not sure.  Is that easy to replace or should I check something else first?