  • Aug 27, 2007, 06:00 AM
    rll1949
    Plex plumbing application
    I recently acquired a large amount of Driscoplex 6500. I understand that it is a gas line but can I also use it for 180degree low pressue boiler water.
  • Aug 27, 2007, 06:35 AM
    iamgrowler
    Quote:

    Originally Posted by rll1949
    I recently aquired a large amount of Driscoplex 6500. I understand that it is a gas line but can I also use it for 180degree low pressue boiler water.

    No.

    Driscoplex has a very low pressure rating (30psi) which is lower than most low pressure hydronic systems.

    Also, the temperature rating of a hydronic system is in excess of the ratings specified by the manufacturers of most medium density polyethylene piping materials (MDPE.

    You would do better to use a high density polyethylene product (HDPE).