    Start capacitor/ run capacitor info
    OK I think I have narrowed my problem down to either a run capacitor or my start capacitor

    My fan on top of my unit runs but the compressor will hum for about 3-5 seconds every 5 minutes or so . Is it possible for my duel run capacitor to let the fan run but not let the compressor run, or is the problem my start capacitor?
  • Aug 19, 2007, 04:49 PM
    esquire1
    Yes it is. If you replace it make sure you replace with the same as in it now i.e. 35/5 or 40/5 etc. The rating is stamped on the capacitor
  • Sep 9, 2013, 09:17 AM
    summertime1001
    Bryant ac tripping breaker. Outside unit fan runs fine, cools house, then after a bit, breaker trips. Any ideas?
  • Sep 10, 2013, 08:09 PM
    Grady White
    Summertime1001: Sounds like you have a compressor going bad. Something is causing the system to draw high amperage & the compressor is the most likely suspect.