Ask Me Help Desk

Ask Me Help Desk (https://www.askmehelpdesk.com/forum.php)
-   Electrical & Lighting (https://www.askmehelpdesk.com/forumdisplay.php?f=105)
-   -   15 a breaker load (https://www.askmehelpdesk.com/showthread.php?t=120434)

  • Aug 17, 2007, 08:41 AM
    ducktruck
    15 a breaker load
    The rating of the breaker say 15 amps , can I pull a load of 15 amps continues, or is the breaker derated by 20%
  • Aug 17, 2007, 08:58 AM
    tkrussell
    If a load runs 3 hours or more it is considered as a continuous load, and the entire circuit, including the circuit breaker is to be loaded no more than 80 % of the circuit rating. So, a 15 amp circuit should have no more than 1440 watts running continuously.