I need some expert assistance...
I think that I have an open neutral on the power company's side. They came out to look at it today and didn't fix anything, and I would like someone else to evaluate my conclusion before I call them tomorrow.
This is a commercial building that I am remodeling. It has been vacant for some time before I bought it. I noticed the problem because my lights were getting dimmer and brighter depending on whether the saw would be running or the air conditioner would kick on. I'm not talking about just dimming when a large load is applied - I'm talking about the air conditioner kicks on and the lights get brighter.
So I started doing a little investigating online to figure out a possible problem and came up with an open neutral. Primarily, this conclusion arose because depending on the load, I am measuring 100 volts on one leg and 140 on the other. (FYI - I did add a couple light circuits and replaced the main breaker box - this is in an area that isn't in city jurisidiction). So today after the city didn't do anything (I wasn't present when they came - building still vacant during remodel), I started checking a little deeper.
Here is the setup: I have a 100 amp outdoor panel after the meter can. That runs to a 100 amp interior panel that I have all the individual circuits on. I turned off all but one breaker and put a 7 amp load on that breaker (vacuum). I started measuring amperage at the interior panel. I have 7 amps leaving the circuit breaker going to the receptacle (for vacuum). Next, on one of my hot leads in to the panel, I am pulling 7 amps. The other lead is not pulling any amperage. No amperage on ground either. There is 7 amps on the white neutral (returning to exterior 100 amp breaker). I go out to the outside panel and 7 amps going to the interior panel on one lead. None on the other and 7 amps on the neutral going to the bus bar where the neutral, service neutral and ground are tied together. There I measure no amps leaving on the service neutral to the meter, but there is 5 amps leaving on the ground (I figure the other 2 are seeping out on the metal conduit). I climbed on the roof and carefully measuring amperage at the weatherhead, there is 7 amps on one lead, none on the other and none and the neutral.
I know that is a LONG explanation, but I guess my main question is am I right in my conclusion that this has to be an open neutral on the power company's side? Every circuit, regardless of whether it is a table saw or a overhead light, causes a voltage shift when it is energized. If it was an open neutral on my side, it wouldn't affect every circuit would it?
Any guidance would be appreciated. I know there are some smart people out there...