    What is more effective in industrial application.. the HRG (high resistant grounding) system or the low resistant grounding system?
  • Jul 27, 2007, 03:01 AM
    tkrussell
    The issue is not effectiveness.

    Where do you come up with these questions?

    If the facility is housing a critical operation, HRG may be considered, as if there is a fault, the fault can be detected with indicators, and not cause the opertion to shut down due to a fuse or breaker opening.

    An LRG system will cause a protection device to open immediately in the event of a ground fault and shut down the circuit.