  • Jul 21, 2007, 05:28 AM
    alloyd
    Goodman AC/Furnace: condenser not coming on after installation of new blower motor
    Have and outside Goodman AC unit and Goodman furnace (inside duh!). Anyhoo, after installing new blower motor the AC unit will not kick on. Have reset outside breaker, and double checking wiring on controller board on furnace, noticed one blue wire was disconnected, reconnected that and still not working.

    New installation >>two connectors on controller board labeled park, that were previously connected on old setup up; consulted a furnace expert, over the phone and said PARK means that they do nothing...

    Blower motor is a three speed>>
    Black (High) is connected to Cool H on controller board
    Blue (Medium) is connected to Heat H on controller board
    Red (Low) capped off
    Yellow ( Line) is connected to Line Neutral on controller board

    Controller Board
    Red and Blue from controller board marked PARK are capped off

    Need help on steps to get AC working again, anything helps!
  • Jul 21, 2007, 10:13 AM
    hvacservicetech_07
    First make sure that you didn't pull any of the low voltage connections loose at the botton of the control board.
  • Jul 21, 2007, 10:24 AM
    NorthernHeat
    Does the inside blower start when you turn the thermostat on cool? Did you follow the thermostat wires from the outside unit back to the furnace and make sure the 2 wires are connected in the furnace?
  • Jul 21, 2007, 11:22 AM
    alloyd
    The inside blower motor does kick on when thermostat is set to cool, yes. The outside is not starting up.
  • Jul 21, 2007, 11:28 AM
    alloyd
    My concern was the two PARK positions on the controller board Goodman
  • Jul 21, 2007, 11:43 AM
    NorthernHeat
    Park terminals are for the unused blower speed wires. I think you knocked the thermostat wires for the condenser off. One goes to the yellow wire from the thermostat and the other one goes to the chassis ground.
  • Jul 21, 2007, 12:13 PM
    alloyd
    Yup that was it! The lead from thermostat was conncected to the TWIN terminal, the only one that did not have a wire connected to it, typical male response, hmmm loose wire, all terminals are connected but this one, (eventhough it says common line) can I get a home DOH! Please do not DEE DEE DEE me, OK? Thanks for the help and prompt answers.