Originally Posted by esquire1
Well, I answered but guess I for got to post. The frezzer is good at -5 and ref shold be around 38-40. Frost is ok on bottom of evap as it will disapate during defrost. I tend to beleive a restriction in duct or damper not fully opening. On occasion I have seen where the light will not go off in ref. Open door and depress door switch to verify it going out. It probably is but we need to check everything. Also possible the cold control but let's check these things out first. Much eaiser to troubleshoot in person but you seem to have knowledge to be able to get through this. Also do you have a meter if we need to go into futher testing?