-   -   Wireing the above ground pool (https://www.askmehelpdesk.com/showthread.php?t=104297)

  • Jun 25, 2007, 05:02 PM
    schmi0
    Wireing the above ground pool
    ... where I'm at...

    Got the conduit..
    Got a nice 20 amp duplex gfi receptacles in metal enclosure.. 1 for pump and one for pool light...
    So , 12/2 and 14/2 on sale @ the depo... both have grounds...
    20 amp fuse breaker
    ... and I should be good?? /
  • Jun 25, 2007, 05:19 PM
    tkrussell
    What is the pump horsepower?

    Also need #8 to ground all the metal within 5 feet of the pool and bring that ground wire back to the lug on the outside of the pump motor.