Ask Me Help Desk

Ask Me Help Desk (https://www.askmehelpdesk.com/forum.php)
-   Other Engineering (https://www.askmehelpdesk.com/forumdisplay.php?f=561)
-   -   Chiller pump (https://www.askmehelpdesk.com/showthread.php?t=103049)

  • Jun 20, 2007, 11:26 PM
    eltayeb92
    Chiller pump
    How to calculate chiller pump head
  • Jun 21, 2007, 01:56 PM
    caibuadday
    Quote:

    Originally Posted by eltayeb92
    how to calculate chiller pump head

    It is the total pressure lost plus 5 to 10 psig: head pressure(vertical piping: you need 0.433 psig to push the water 1 ft height or 1 ft of water,WC, is equal to 0.433 psig)... horizontal piping( it rate in ft of water at per 100ft of pipe) and its associated valves and fittings, and the coil.. . plus you need to know what is your design (intended) flow, you need to get a hold of the chart for friction lost for your pipe and fittings and valves