  • Jun 20, 2007, 04:21 PM
    volan
    'C' connection on new thermostat
    I am considering purchasing a Honeywell W8665A remote control thermostat. I have the wiring diagram and I am a bit confused. I'm hoping someone can help me.

    My current thermostat attached to the wall has the following wires available:
    Y, G, R, W.

    The manual for the W8665A states that C must be connected, but I have no 'C'. Apparently the C is a common coming off the transformer.

    Am I out of luck or is there a way around it?
  • Jun 20, 2007, 05:57 PM
    hvacservicetech_07
    I'm pretty sure you'll need a common to power that thermostat, if all you have is four wires sticking out of the wall, simply pull a 5 ct cable and hook the common up on the furnace, this may be pretty easy if they didn't attach the wire to a stud inside the wall, just connect the new wire and old and pull it down through the wall.
  • Jun 20, 2007, 09:20 PM
    volan
    Thank you. I'm not confident pulling a cable from the basement up to the 2nd floor of my house. Perhaps I'll consider professional help.

    But at lease now I know that I need the 'C' wire and I won't rush into buying the unit until I know what I'm going to do.

    Thanks again.
  • Jun 20, 2007, 09:22 PM
    hvacservicetech_07
    Is there a reason that you want that thermostat? There are some nice stats on the market that would work just fine, and they have a nice look.
  • Jun 20, 2007, 09:28 PM
    hvacservicetech_07
    Keep in mind, it wouldn't cost you very much to call in a pro to pull a new wire and install the thermostat, your talking an hour labor or less.
  • Jun 21, 2007, 07:09 AM
    volan
    Quote:

    Originally Posted by hvacservicetech_07
    Is there a reason that you want that thermostat? There are some nice stats on the market that would work just fine, and they have a nice look.

    The current thermostat is located in a hallway in front of a big picture window so the temperature reading is not what the temperature in the rooms are. That's why I wanted a remote control thermostat. That way I can put the sensor in one of the rooms and the temperature control will be more accurate.
  • Jun 21, 2007, 07:11 AM
    volan
    Quote:

    Originally Posted by hvacservicetech_07
    Keep in mind, it wouldn't cost you very much to call in a pro to pull a new wire and install the thermostat, your talking an hour labor or less.

    Only an hour? I'll check into it. Thanks.
  • Jun 21, 2007, 08:58 AM
    biggsie
    The transformer supplies 24 vac (C is common for 3 relays -- cooling --heating -- fan and common for thermostat power Fig.2 The other leg is R which provides
    Power to thermostat, and is jumpered to RZ terminal...


    http://customer.honeywell.com/techli...0s/69-1630.pdf

    Inside wall would be good location for thermostat Maybe a new run would work...
  • Jun 21, 2007, 09:08 AM
    volan
    Yes, I plan to put the thermostat in one of the rooms away from direct sunlight
  • Jun 21, 2007, 03:14 PM
    tazdec
    Quote:

    Originally Posted by volan
    I am considering purchasing a Honeywell W8665A remote control thermostat. I have the wiring diagram and I am a bit confused. I'm hoping someone can help me.

    My current thermostat attached to the wall has the following wires available:
    Y, G, R, W.

    The manual for the W8665A states that C must be connected, but I have no 'C'. Apparantly the C is a common coming off the transformer.

    Am I out of luck or is there a way around it?

    See if your stat reads power stealing if not you need a common to the stat see if you have a extra wire in your stat wire if you do you can hook up c at the unit and the c at the stat
  • Jun 21, 2007, 03:29 PM
    volan
    Quote:

    Originally Posted by tazdec
    see if your stat reads power stealing if not you need a common to the stat see if you have a extra wire in your stat wire if you do you can hook up c at the unit and the c at the stat

    Thanks for your post.

    I don't actually have the thermostat yet. I'm just doing my due diligence prior to purchasing it. I find that doing work upfront results in less frustration afterwards.

    The only wires I have at the T-stat are those that I have mentioned. There do not appear to be any spare wires that I can see.