central indoor fan blower not working
Hi,
My indoor blower quit working, first it made weird sounds during start few times and then quit. I have a Rheem Criterion furnace from 1992. The air handler and evaporator was replaced few years ago and other maintenance done.
The run capacitor (Old one was a cylindrical 15MFD 370VAC and new one is oval GLOBAL 2010 15x370)was replaced yesterday night and fan started working after about 20-30 secs. We were very happy. We just came back from dinner and it has died again.
Blower control board from other unit was tried but motor just hums like it did before new capacitor.
Should I get the fan relay replaced? What seems to be blowing the capacitor? I have already had couple of service calls in month and would like to get this fixed good at least for one season.
Thanks for reading and any suggestions.
ulbhpy