Getting ready to pipe in a new pressure switch for a Franklin submersible pump, and I'm having trouble understanding how to set low pressure pump on, and high pressure pump off limits. Anyone know how to choose and set these limits?
Getting ready to pipe in a new pressure switch for a Franklin submersible pump, and I'm having trouble understanding how to set low pressure pump on, and high pressure pump off limits. Anyone know how to choose and set these limits?
Most well pressure switches come set at either 30/50 or 40/60. The larger nut or bolt adjust both the start and stop pressures up by tightening or lower by loosening. To change from 30/50 to 40/60 tighten the larger nut
The smaller nut or bolt changes the difference between the on and off. To go from 30/50 to 30/60 tighten the smaller nut or bolt.
Look under the cap of the switch. It will tell you what nut to turn to do what you want.