  • Jan 5, 2009, 02:11 AM
    RockyMtnHigh
    Placement of AAV
    Long story short our kitchen sink in our house needs an AAV as a result of a renovation. My question is to the exact location of the AAV downstream from the p-trap. Thank you in advance for any advice.

    RMH

    Option 1. Place it ontop of the "T"

    AAV
    L
    l--------------------P-Trap
    l
    l
    l

    Or...

    Option 2. Downstream of Ptrap but before elbow

    AAV
    L
    ------------l---------P-Trap
    l
    l
    L
    L
  • Jan 5, 2009, 05:10 AM
    massplumber2008
    1 Attachment(s)
    Hi RMH:

    The AAV should be located within a few feet of the p-trap. It can be piped on the horizontal at least 6-12" above the pipe (picture 1 on left), or it can be on top of the vertical pipe above the ptrap (picture 2 on right). The AAV must remain accessible in case it needs to be changed in the future.

    Let me know if need more...

    MARK
  • Jan 5, 2009, 08:57 AM
    speedball1
    Quote:

    Originally Posted by RockyMtnHigh View Post
    Long story short our kitchen sink in our house needs an AAV as a result of a renovation. My question is to the exact location of the AAV downstream from the p-trap. Thankyou in advance for any advice.

    RMH

    Option 1. Place it ontop of the "T"

    AAV
    l
    l--------------------P-Trap
    l
    l
    l

    or....

    Option 2. Downstream of Ptrap but before elbow

    AAV
    l
    ------------l---------P-Trap
    l
    l
    l
    l

    How's this grab you? (see image) Good luck, Tom
  • Jan 5, 2009, 12:04 PM
    dclynch
    Are AAVs allowed in Mass residential codes?
  • Jan 5, 2009, 04:05 PM
    massplumber2008
    Hi Dennis...


    NO... AAVs are NOT allowed in Massachusetts residentially or commercially.

    You can appeal to the local plumbing inspector for a variance, but I have only seen 1 approved in 26 years!

    Let us know if need more here...

    MARK