  • Feb 16, 2014, 12:43 PM
    lexefx
    White rogers control swap 50e47-060 to 50e47-843 Fan works manual, not auto.
    Furance is a Trane XE70. Original boad went intermitent shut-down. Swapped to 843. Green light running. When it's on auto furnace kicks on, fan does not.In about 90-120 seconds I then think it thermals and shuts off. Works perfect with the fan on manual on mode. Is there a fan turn on wire I am missing? Any help appreciated.
  • Feb 16, 2014, 08:17 PM
    Grady White
    The 50E47-843 is the replacement suggested by White-Rodgers. You have possibly disonnected a fan control wire, you may have a bad fan control, or the heating speed on the motor could be bad. If you can provide a wiring diagram of the furnace we can probably help you track down the problem.
  • Feb 17, 2014, 06:06 AM
    WallyHelps
    Did a short jumper wire come with the new board?
    I replaced a board on a Trane furnace (unfortunately, different board number) and needed to jumper between RO1 and RO2 on the 12-pin connector.

    Consult the installation instructions to see if this might apply to your board.

    Good luck,
    WallyH
  • Feb 17, 2014, 03:29 PM
    Grady White
    No 12 pin connector on this module.
  • Apr 14, 2014, 01:45 PM
    lexefx
    I decided to mess with this again. Auto fan works with AC, but not with the furnace. Isn't a thermostat in charge during AC only? What controls the fan turn on in auto furnace mode.
  • Apr 14, 2014, 01:57 PM
    lexefx
    Quote:

    Originally Posted by Grady White View Post
    The 50E47-843 is the replacement suggested by White-Rodgers. You have possibly disonnected a fan control wire, you may have a bad fan control, or the heating speed on the motor could be bad. If you can provide a wiring diagram of the furnace we can probably help you track down the problem.

    How would I get you this diagram? The rogers-white tech guy said there is no turn on wire for this module. I didn't end up with any loose wires, all were transferred over per their diagram/conversion chart.