Ask Me Help Desk

Ask Me Help Desk (https://www.askmehelpdesk.com/forum.php)
-   Electrical & Lighting (https://www.askmehelpdesk.com/forumdisplay.php?f=105)
-   -   110 outlet stops working, NOT tripping any circuit breaker. (https://www.askmehelpdesk.com/showthread.php?t=136218)

  • Oct 2, 2007, 08:35 AM
    pgffgp
    110 outlet stops working, NOT tripping any circuit breaker.
    I have a 220 outlet three feet from a 110 outlet.

    When I am using a clothes washer on the 110, it goes dead after a while (10-30 minutes).

    No breaker is tripped.

    When I turn on the 220 clothes dryer, the 110 washer restarts from where it left off.
  • Oct 2, 2007, 08:56 AM
    tkrussell
    Sounds like the 120 volt outlet is connected to the 240 volt outlet for power, which is a violation.

    Also sounds like the neutral wire connection is loose, probably in the dryer outlet.

    Do not continue to use this arrangement until , first the loose connection is found, as this may damage the washer, or the connection will get worse and heat up and cause a fire.

    Second, if the 120 volt oulet is connected to the dryer 240 volt outlet for power, consider having a new 120 volt circuit installed for the washer outlet.