    UP-Flush piping construction on a 90 bend please help
    Hello

    I have an upflush in basement the discharge pipe goig up and then 90 bend

    Heed help how to properly configure this set up Please tell me which is best way to set this up from pictures below

    Attachment 47283Attachment 47284Attachment 47285
  • Apr 6, 2015, 07:33 AM
    speedball1
    Please explained exactly what it is you wish to do. Back to you, Tom
  • Apr 6, 2015, 07:37 AM
    notlike7
    UP-FLUSH discharge going up than gravity drain

    Look at pictures let me know what is the best way to construct the 90 degree bend, from UP-flushing bending 90 to gravity drain
  • Apr 6, 2015, 11:25 AM
    massplumber2008
    Use the long sweep 90 degree fitting at top... no need to use a trap or clean out here. Then, connect the drain pipe to a large drain pipe using a wye and a clean out.

    Mark
  • Apr 6, 2015, 12:09 PM
    Mike45plus
    I would also include an isolation valve, check valve, and union...
  • Apr 6, 2015, 12:34 PM
    massplumber2008
    An isolation valve and a union are always a good idea (requirement) on these, but all macerator pumps I've ever installed have an internal check valve so that should not be needed here. Of course, if you check the installation manual you will see manufacturer recommendation for drain AND vent requirements!

    Good luck!

    Mark