    My R-410 system is reading 400 on high side and 133 on the low side. Problem?
    My R-410 system is reading 400 on the high side and 133 on the low side. The typical readings should be 418 and 130 respectively. What may be a cause of this? We are experiencing lots of condensation and a unit that never cycles. All coils have been cleaned and the filter replaced.
  • Aug 11, 2013, 05:12 PM
    Joshdta
    Seems high side is to high should be around 375 for 135 suction. What is temp outside? Sounds over charged or bad txv in coil