  • Oct 6, 2012, 07:54 AM
    GhouseAamiri
    Hydraulic Elevator motor
    What is meant by" intermittent 40% " in hydraulic elevator motor
  • Oct 7, 2012, 03:46 AM
    tkrussell
    Indicates minimum size of overload and branch circuit sizing.
  • Oct 7, 2012, 04:10 AM
    GhouseAamiri
    Hydraulic Elevator Motor
    Dear Mr.TK Russel,thanks for your answer.Iam still not clear.Please could you shed more light on your answer.If I am not wrong ,is it "intermittent 40%" indicates 40% more can be loaded than to the rating of the motor.###THANKS
  • Oct 8, 2012, 03:20 AM
    tkrussell
    In USA, we use the NEC, and it allows us to use smaller overload protection and conductors by 40% of the full running load amps.

    We do not load the motor 40% over the rated load of the motor.
  • Oct 8, 2012, 04:39 AM
    GhouseAamiri
    Hydraulic Elevator motor
    Thanks a lot,Mr.TK Russel