What is meant by" intermittent 40% " in hydraulic elevator motor
What is meant by" intermittent 40% " in hydraulic elevator motor
Indicates minimum size of overload and branch circuit sizing.
Dear Mr.TK Russel,thanks for your answer.Iam still not clear.Please could you shed more light on your answer.If I am not wrong ,is it "intermittent 40%" indicates 40% more can be loaded than to the rating of the motor.###THANKS
In USA, we use the NEC, and it allows us to use smaller overload protection and conductors by 40% of the full running load amps.
We do not load the motor 40% over the rated load of the motor.
Thanks a lot,Mr.TK Russel