    Free space around a panel
    I'm building a new house, and just finished with the electrical inspection.

    Today, I get to the site, and the HVAC people have run ductwork right next the panels in the basement.

    http://i212.photobucket.com/albums/c...i95/Panel1.jpg

    The panel on the right is the main panel, the one on the left is a 60 AMP sub panel.

    The clear space rules for panels (as I remember them anyway) say a width of 30 inches and a minimum height of 78 inches. It doesn't say anything about whether that is centered on the panels or what.

    Does it look like this will still pass or do I need to get the HVAC stuff moved?

    John
  • Dec 28, 2007, 06:11 AM
    tkrussell
    No, the 30 " dedicated space does not need to be centered on a panel, it can start from the edge of the panel.

    So you should be OK.