Originally Posted by Stratmando
The neutral with all breakers off, still should not have amps, and more likely not the Electric Company.
A circuit has to be complete to draw power, with breakers off circuit to neutral is open.
Is you neutral bonded to ground in panel.
also, with breakers on, measure current of both hots, neutral, and ground.
The neutral should draw the difference of the 2 hots. the ground should be Zero,
If ground is drawing current. turn off breakers 1 by 1 to determine equipment or circuit leaking to ground.
Are you using clamp on ampmeter around neutral in main panel?