Ask Me Help Desk

Ask Me Help Desk (https://www.askmehelpdesk.com/forum.php)
-   Heating & Air Conditioning (https://www.askmehelpdesk.com/forumdisplay.php?f=150)
-   -   AC not working on heat pump (https://www.askmehelpdesk.com/showthread.php?t=350037)

  • May 5, 2009, 10:41 AM
    zanec
    AC not working on heat pump
    I have a AC unit that's not working and it's a heat pump. When it's in cooling mode, the condenser fan motor doesn't work but the compressor does. Then it shuts down on high pressure. First thing I think that it's a bad condenser fan motor or maybe a cap. Since it's a heat pump, I probably should have checked to see if the condenser fan worked in the heat mode, right? Because they said the heat worked. I think it might be the circuit board in the condenser. What do you think?
  • May 5, 2009, 01:39 PM
    TristaNicholle

    The defrost board could be controlling the fan, but odds are that it's a bad capacitor...
  • May 7, 2009, 05:20 AM
    dac122

    Replacing the cap is a cheap and easy fix. If that doesn't do it and the motor is good you're only left with a controlling board as a fault.

  • All times are GMT -7. The time now is 11:12 AM.