-   -   Installed new thermostat, now a/c outside unit will not run (https://www.askmehelpdesk.com/showthread.php?t=345996)

  • Apr 25, 2009, 03:06 PM
    eliz310
    Installed new thermostat, now a/c outside unit will not run
    We installed a Honeywell RTH6400 thermostat in January. We now need a/c & outside unit will not come on, inside unit runs. When we installed this we thought everything was hooked up right, but who knows. We've pulled the cover off the thermostat & we have a blue wire that is taped, should it be hooked up to something? Is this a different issue all together?
  • Apr 25, 2009, 03:16 PM
    Joshdta

    Do you have a jumper wire between rh and rc?
  • Apr 25, 2009, 03:18 PM
    eliz310

    Metal jumper wire is connected to R & Rc.
  • Apr 25, 2009, 03:19 PM
    Joshdta

    Do you have a volt meter?
  • Apr 25, 2009, 03:20 PM
    eliz310

    No, My father does, but not here. I just looked & the red wire is on Rc. Is this correct?
  • Apr 25, 2009, 03:23 PM
    Joshdta

    Yes as long as it has a jumper. Set the t-stat so the ac should come one. Then go outside and take the 2 screws holding the panel to the electric on the ac. Right where the power goes in. look for this contactor.

    http://yueqing-shi-shinaidi-electric...ges/283101.jpg

    See if the two bottons in the middle are pushed in.
  • Apr 25, 2009, 03:25 PM
    Joshdta

    Did you check the breaker to the outdoor unit?
  • Apr 25, 2009, 03:25 PM
    eliz310

    Checking will be right back.
  • Apr 25, 2009, 03:26 PM
    Joshdta

    Rember that is 220 volts so be careful you can push those buttons with a screw driver.
  • Apr 25, 2009, 03:27 PM
    eliz310
    Not finding where the power goes in.
  • Apr 25, 2009, 03:29 PM
    eliz310

    We reset breaker to unit earlier & no success.
  • Apr 25, 2009, 03:30 PM
    Joshdta

    Should be on the back left or the back right of the unit closest to the house.
  • Apr 25, 2009, 03:31 PM
    eliz310

    Already tried resetting the breaker..
  • Apr 25, 2009, 03:32 PM
    eliz310

    Is it a the entire back of the unit?
  • Apr 25, 2009, 03:39 PM
    Joshdta

    Not sure, what brand do you have?
  • Apr 25, 2009, 03:40 PM
    eliz310

    Lennox
  • Apr 25, 2009, 03:42 PM
    Joshdta

    Yes some lennox and trane units you have to take the entire pannel off.
  • Apr 25, 2009, 03:43 PM
    eliz310

    Ok, will do
  • Apr 25, 2009, 04:03 PM
    eliz310

    There is only 1 black button & it seems to be pushed in
  • Apr 25, 2009, 04:05 PM
    Joshdta

    OK if it is pushed in then your t-stat is working corectly. Your problem is with your main power. 220 volt. Is there a outside disconnect for the main power on your house?