Comment on jlisenbe's post
Yes, coming from the holding tank. That is why I wanted to know if the heat was coming from the supply line as it emerges from the casing, first. It doesn't make sense to me either.
Comment on jlisenbe's post
Once pizza was put on the line I figured this topic was getting serious and almost dangerous. I don't know why my well is wired this way. There is space on the pressure switch to disconnect both hot legs and kill all power to the pump. I figured the installer was either lazy or didn't know what they were doing. I guess rewiring this will just get added to my summer to-do list.
Comment on jlisenbe's post
Yes, only one of the hot legs went through the switch and the other is wired directly to the pump. When the wire shorted it completed the circuit. Not enough power to run the pump, but enough to turn it into a heater. Why this was wired this way is beyond me, but it will be corrected.
Comment on jlisenbe's post
Nope the red wire. Two pole breaker. I personally have not seen a 120 volt submersible pump, but that doesn't mean they're out there.