I have a carrier gas furnace model 58DP100 . The fan runs continuously and the gas burners will not ignite ( the pilot is lit ) HELP... please .
I have a carrier gas furnace model 58DP100 . The fan runs continuously and the gas burners will not ignite ( the pilot is lit ) HELP... please .
You have a limit open more than likely. Check/Change your filter first. Check for 24 volts between the posts on the limit (small rectangle facing you on firewall of furnace with 2 wires coming out). Other limits may be open as well. You may be able to reset the limit, but you also need to correct the reason it tripped-it's a safety device. If you haven't had it looked at for a while by a tech, now would be the time to do so.Quote:
Originally Posted by billinric
Thanks for your help, it was a tripped limit, just not that particular one. We're warm and cozy again !
Help just where is that limit switch located? I pressed the one on top of the furnace. Still no heat. Furnace was working until this weekend.