    Heating & Cooling Maintenance, Repair & Troubleshooting FAQ from NortherHeat
    Check out these tips and explanations, below, from our Heating and Cooling Expert. Of course, you're also welcome to post questions to this board for more information: Just click the "Ask about Heating & Air Contidioning" button at the top of the page.
  • Jan 28, 2007, 12:29 PM
    NorthernHeat
    Always use proper electrical safety: see here and remember, "if it isn't grounded it isn't dead"

    General
    1. Should I have the fan switch turned to "ON" or "AUTO".
    2. Thermostat wire color codes explained.
    3. Some additional thermostat resources.
    4. What is a heat pump?
    5. How do I know what the efficiency of my furnace is?
    6. How do I know what type of ignition I have?
    7. How do I know if the problem is in the thermostat?
    8. What information should I include in my post?
    9. Where is the fuse?
    10. Is my furnace overheating?
    11. What is a plenum?
    12. How do I light the pilot light?


    Gas forced air.
    1. Sequence of operation.
    2. Blower turns on but there is no heat.
    3. What is a flame sensor?
    4. What is a pressure switch?
    5. Where is the diagnostic light?
    6. What is a transformer?
    7. What is a main limit?
    8. What is a roll out limit?
    9. What is a spill switch?


    Hydronics, boilers.
    1. Why do I hear water running in the pipes?
    2. What is a zone valve?
    3. What is a pressure reducing valve?
    4. What should the pressure gauge read?
    5. How do I purge the air out of my radiators?
    6. What is the expansion tank?
    7. What is a back flow preventer?
    8. How do I know if the circulating pump is running?


    Air conditioning.
    1. What is the condensing unit?
    2. What is the evaporator coil?
    3. What is a compressor?
    4. How cold should my registers be?
    5. Does my air conditioner use my furnace to operate?


    Heat pumps.
    1. How warm should my registers be?
    2. Why is there steam or smoke coming from my heat pump?
    3. The fan in the outside unit stopped running?
    4. Why does my heat pump make strange noises from time to time?
    5. What is the Aux and Emergency lights on my thermostat for?
    6. There is a button on the outside unit...Why do I have to keep pushing it?


    Component identification.
    1. Gas valve
    2. Main limit
    3. Flame sensor
    4. roll out limit/spill switch
    5. Draft inducer blower
    6. Vacuum switch
    7. Hot surface ignitor
    8. Heat exchanger
    9. transformer


    Online resources.
    1. Honeywell Thermostats your home expert.
    2. Robertshaw customer support.
    3. Rheem Furnaces
    4. American Standard/Trane.
    5. York
    6. Aprilaire, air cleaner, humidifiers, dehumidifiers and ERV's.


    More to come.



    If my answer helped, please click Rate this Answer! Below. Thanks!
  • Jan 28, 2007, 12:35 PM
    NorthernHeat
    Thermostat wire color codes explained.
    Please note. Not all installers use the proper color codes when they install or replace equipment. It may be necessary go go to the furnace or outdoor unit to verify what wires are for what purpose. Also be sure there are no splices in the wire that could change the wire colors between components.

    • R (red) or Rh (Red heat) 24 volts from equipment.
    • Rc (Red cooling) 24 volts from transformer in cooling equipment.
      Note: If only furnace has a transformer and cooling equipment does not jumper Rc and Rh.
    • W (White) sends 24 volts to furnace control to start the heating cycle.
    • W2 (no standardized wire color, usually whatever wire color is available) controls second stage heat.
      Note: W2 is most often used for heat pumps to control what is called emegency heat or Auxillary heat, and most often will use the white wire.
    • Y (yellow) often (blue) is used, controls cooling unit (outdoor condensing unit) also is used for heat pump heat.
    • Y2 (no standardized wire color, usually whatever wire color is available) controls second stage cooling.
    • G (Green) controls the fan "on" operation of the furnace/air handler. Also often is used to start the blower for many electric furnaces.
    • C (common) most often brown but can also be black or other color available to installer.
    • O (orange) Energizes heat pump reversing valve for cooling (Trane and most other brands).
    • B (Blue) Energizes heat pump reversing valve for heating (Rheem, Ruud and Weatherking).


    How to connect the wires to a new digital thermostat.

    Back to top

    If my answer helped, please click Rate this Answer! Below. Thanks!
  • Jan 28, 2007, 01:10 PM
    NorthernHeat
    What is a heat pump?

    A heat pump is an air conditioner that can change refrigerant direction.
    Just as an air conditioner absorbs heat inside the home in the summertime and expels it outside. In the winter a heatpump reverses refrigerant flow, absorbs heat outside and expels it inside the home for heat.

    Heat pumps are very efficient when compaired to other heating sources. However when the outdoor temperature falls very low, lets say below 25 degrees F. there is very little heat outside to absorb and their efficiency decreases.

    Temeratures from the register will typically be around 90 degrees F. Thus people often feel as though their furnace is blowing cool air. Because of this low vent temperature a heat pump will run a long time to keep a home warm.

    The outdoor section of the heat pump becomes very cold and will form frost, and even some ice. To correct this problem the heatpump will go into a defrost cycle to clear itself from all this frost. Basically it is running like an air conditioner now. Often steam will be seen when it is defrosting, the outdoor fan stops turning and the back-up heat source will start to offset the fact that the air conditioner is now on.

    The heat pump should be installed up high on stands to keep it out of the snow, and give all the defrosted water a place to go.

    All heat pumps with a back up heat source (this is all cold climates) need a 2 stage heat, pump, thermostat, or other electrical modifications must be made to the out door unit to work properly.


    Back to top


    If my answer helped, please click Rate this Answer! Below. Thanks!
  • Jan 28, 2007, 01:22 PM
    NorthernHeat
    How do I know what efficiency my furnace is?

    Furnaces that have a simple metal vented system with no draft blower are around 70 percent efficient. Simply known as natural draft.

    Furnaces with a metal flue pipe and a blower motor that exhausts the flue gasses are 80 percent efficient or above. Simply called 80+.

    Furnace with induced draft blowers and PVC flue pipes are 90 percent and above. Simply called 90+.


    Back to top


    If my answer helped, please click Rate this Answer! Below. Thanks!
  • Jan 28, 2007, 01:32 PM
    NorthernHeat
    What type of ignition do I have?

    Standing pilot.
    Pilot light that is constantly lit. Typical in older furnaces, uses this flame to ignite the main burners.

    Intermittent pilot
    Pilot light ignites each time the furnace starts.
    Two main types are
    1. glow plug (called a hot surface ignitor) ignites the pilot light.
    2. spark (a small electrical spark) ignites the pilot light.

    Direct ignition
    Similar to intermittent pilot in that a spark or hot surface ignitor is used to light the burners, most common method in newer furnaces.


    Back to top

    If my answer helped, please click Rate this Answer! Below. Thanks!
  • Jan 28, 2007, 01:45 PM
    NorthernHeat
    How do I know if the problem is in the thermostat?

    Disconnect power at the furnace or breaker box.

    Remove thermostat from wall and jump R (Red) to W (White)
    Restore power, did the furnace start to run? If yes the thermostat was bad. If no the problem is in the thermostat wire or furnace.

    Disconnect power to furnace again. At the furnace find out how the thermostat is connected to the controls. Again jumper R and W. Retore power. Did the furnace start? If yes the problem was the wire if no the problem is in the furnace.

    Using a volt ohm meter. Turn the thermostat to heat, turn it up above the room temperature, at the furnace check for 24 volts betweem W and common, chassis, ground, if 24 volts is present at W the thermostat is working fine.

    Same method can be used for fan (G)
    And cooling (Y)

    Red wire should have 24 volts at all times.

    Note Most furnaces have a safety door switch for the blower compartment, this button must be depressed to power on the furnace.



    Back to top

    If my answer helped, please click Rate this Answer! Below. Thanks!
  • Jan 28, 2007, 02:32 PM
    NorthernHeat
    What information should I include in my post?

    Age of equipment, best you can tell...
    Brand (Manufacturer)...
    Efficiency... see here
    Natural gas, LP, forced air, boiler, heat pump, air conditioner...
    Package unit (A/C and heat in one unit), split system, (furnace inside A/C outside)...

    What does it do? Not do?

    Back to top



    If my answer helped, please click Rate this Answer! Below. Thanks!
  • Jan 29, 2007, 08:04 AM
    NorthernHeat
    Sequence of operation.

    Natural draft furnace.
    24 vollts is always present to the thermostat R terminal.
    1. When the thermostat closes its switch to call for heat, 24 volts is sent out of the thermostat on the W terminal.
    2. This 24 volts goes back into the furnace, then typically through 1 or 2 safety devices to the gas valve.
    3. If the standing pilot is lit. The gas valve opens, and the gas to the burners is then ignited by the pilot light.
    4. The heat exchanger is heated untill a device tells the blower to come on, usually a fan and limit control. Also see camstat fan and limit control.
    5. When the thermostat is satisfied, the switch in the thermostat opens, the gas valve closes, stopping fuel and the fan continues to blow untill the fan and limit cools, turning off the blower.


    High efficiency operation.
    24 vollts is always present to the thermostat R terminal.
    1. Thermostat sends 24 volts through white wire to furnace.
    2. Furnace checks pressure switch, and safety switch's for proper positions (open/closed).
    3. Draft inducer blower motor, starts to run.
    4. If vent and vacuum hoses are clear the pressure switch, closes. (only a few pressure switch's open to prove venting)
    5. After inducer plower purges the heat exchanger, either a pilot lights, a hot surface ignitor (HSI), or a spark begins.
    6. If the furnace is an intermittant pilot model, once the pilot lights, current is sent through the flame by a flame sensor, if current is present through the flame the main gas valve opens and the burners ignite.
    7. If the furnace is direct ignition, The HSI or spark ignites the flame. A flame sensor passes current through the flame, if current is present the main gas valve stays open and heat exchanger begins to warm up.
    8. Most high efficiency furnaces then use an electronic timer on the circuit board to start the blower after the burners are proved.
    9. Thermostat opens when desired temperature is reached.
    10. The gas valve closes, burners extinguish, and the timer starts again to turn off the fan.




    Back to top

    If my answer helped, please click Rate this Answer! Below. Thanks!
  • Jan 29, 2007, 08:34 AM
    NorthernHeat
    3 Attachment(s)
    Typical draft inducer blower motor.



    Back to top

    If my answer helped, please click Rate this Answer! Below. Thanks!
  • Jan 29, 2007, 08:46 AM
    NorthernHeat
    2 Attachment(s)
    Camstat fan and limit control.



    Back to top

    If my answer helped, please click Rate this Answer! Below. Thanks!
  • Jan 29, 2007, 08:47 AM
    NorthernHeat
    1 Attachment(s)
    Fan canter.



    Back to top

    If my answer helped, please click Rate this Answer! Below. Thanks!
  • Jan 29, 2007, 08:48 AM
    NorthernHeat
    2 Attachment(s)
    Honeywell fan and limit control.


    Back to top

    If my answer helped, please click Rate this Answer! Below. Thanks!
  • Jan 29, 2007, 08:49 AM
    NorthernHeat
    1 Attachment(s)
    Fusable link.



    Back to top

    If my answer helped, please click Rate this Answer! Below. Thanks!
  • Jan 29, 2007, 08:50 AM
    NorthernHeat
    2 Attachment(s)
    Main limits.



    Back to top

    If my answer helped, please click Rate this Answer! Below. Thanks!
  • Jan 29, 2007, 08:52 AM
    NorthernHeat
    3 Attachment(s)
    Pressure switch



    Back to top

    If my answer helped, please click Rate this Answer! Below. Thanks!
  • Jan 29, 2007, 08:53 AM
    NorthernHeat
    2 Attachment(s)
    Relay


    Back to top
    If my answer helped, please click Rate this Answer! Below. Thanks!
  • Jan 29, 2007, 08:54 AM
    NorthernHeat
    1 Attachment(s)
    Standing pilot



    Back to top


    If my answer helped, please click Rate this Answer! Below. Thanks!
  • Jan 29, 2007, 08:55 AM
    NorthernHeat
    1 Attachment(s)
    Vacuum port and drain on a 90+ draft inducer blower housing.



    Back to top


    If my answer helped, please click Rate this Answer! Below. Thanks!
  • Jan 29, 2007, 08:59 AM
    NorthernHeat
    2 Attachment(s)
    Hot surface ignitor



    Back to top

    If my answer helped, please click Rate this Answer! Below. Thanks!
  • Jan 29, 2007, 09:13 AM
    NorthernHeat
    1 Attachment(s)
    Flame sensor


    Back to top

    If my answer helped, please click Rate this Answer! Below. Thanks!
  • Jan 29, 2007, 09:33 AM
    NorthernHeat
    1 Attachment(s)
    Thermocouple



    Back to top


    If my answer helped, please click Rate this Answer! Below. Thanks!
  • Jan 29, 2007, 09:33 AM
    NorthernHeat
    1 Attachment(s)
    Gas valve (Standing pilot model)



    Back to top

    If my answer helped, please click Rate this Answer! Below. Thanks!
  • Jan 29, 2007, 09:37 AM
    NorthernHeat
    2 Attachment(s)
    Capacitors



    Back to top

    If my answer helped, please click Rate this Answer! Below. Thanks!
  • Jan 29, 2007, 09:37 AM
    NorthernHeat
    1 Attachment(s)
    Purge and balance



    Back to top

    If my answer helped, please click Rate this Answer! Below. Thanks!
  • Jan 29, 2007, 09:38 AM
    NorthernHeat
    2 Attachment(s)
    Circuit boards



    Back to top

    If my answer helped, please click Rate this Answer! Below. Thanks!
  • Jan 29, 2007, 10:07 AM
    NorthernHeat
    Blower turns on but there is no heat.

    Thermostats only control a fan relay, fan center or circuit board to turn on the blower motor.

    Although these relay's are necessary for cooling to work, they have nothing to do with the heating operation or outdoor cooling section of the equipment.

    Electric furnaces may or may not use this relay controlled by the fan switch of the thermostat.


    Back to top

    If my answer helped, please click Rate this Answer! Below. Thanks!
  • Jan 29, 2007, 10:36 AM
    NorthernHeat
    What is a flame sensor?

    The flame sensor, seen here is typically located in front of the pilot or one of the burner flames.
    It is used as a safety device that insures a flame is present.

    When a flame is present the sensor passes a small electrical current through the flame and tells the circuitry what to do.
    If the sensor gets dirty the current passing through the flame is to weak for the circuitry to work properly.

    To clean the flame sensor, disconnect power to the furnace, remove the flame sensor, clean it with some crumpled up aluminum foil or some very fine sandpaper or steel wool.
    Reinstall it and reconnect the power to the furnace.



    Back to top

    If my answer helped, please click Rate this Answer! Below. Thanks!
  • Jan 29, 2007, 10:48 AM
    NorthernHeat
    What is a pressure switch?

    Pressure switch's are a safety device.
    They insure the flue pipe and inducer draft blower motor are functioning correctly.

    If the flue pipe becomes obstructed, or the inducer fails to start, the furnace will not ignite.
    Also be aware, if the vacuum hose or vacuum ports become obstructed, or fill with water, the furnace will not start.

    Often furnaces are installed with improper flue pipe sizes and can take a year or two for the problem to surface.

    Sometimes the pressure switch can simply go bad and need replaced.


    Back to top

    If my answer helped, please click Rate this Answer! Below. Thanks!
  • Jan 29, 2007, 10:56 AM
    NorthernHeat
    Where is the diagnostic light?

    Diagnostic lights are typically found on the circuit board.
    If the circuit board detects there is a problem the lights will begin to blink a code. Ex... 3 blinks and a pause, then 3 blinks-pause again, and so on.

    The codes are then located on one of the doors, the circuit board or in the blower compartment, describing the problem.

    Note... on most furnaces when the power is turned off, these codes are lost, you will have to wait until the furnace malfunctions again to retrieve the diagnostic code.



    Back to top

    If my answer helped, please click Rate this Answer! Below. Thanks!
  • Jan 29, 2007, 11:05 AM
    NorthernHeat
    Where is the fuse?

    There are several fuses used in most furnaces.

    Fuses protect wiring and components from receiving to many amps or power.

    High voltage fuses can be in a breaker box or fuse panel.
    They can also be located on the side of the furnace by the switch that looks like a light switch, typically called an SSU.

    Low voltage fuses can be on the circuit board or in what is called a fuse holder.
    Fuse holders are typically found in the 24 volt wire leading from the transformer.
    Note... Many digital thermostats also have a fuse in them.

    When a fuse blows, quite often, there is a reason. Either a wire has short circuited to ground or a component has failed.


    Back to top

    If my answer helped, please click Rate this Answer! Below. Thanks!
  • Jan 29, 2007, 11:10 AM
    NorthernHeat
    What is a transformer?

    Transformers are devices that typically step down voltage in an appliance.

    In most furnaces they step 120 volts down to 24 volts.

    The 24 volts then is used as control voltage to the thermostat, other safety devices and relays in the furnace or air conditioner.



    Back to top

    If my answer helped, please click Rate this Answer! Below. Thanks!
  • Jan 29, 2007, 11:14 AM
    NorthernHeat
    What is a main limit?

    Main limits are safety devices. When they get to hot, they open and turn off the gas.



    Back to top

    If my answer helped, please click Rate this Answer! Below. Thanks!
  • Jan 29, 2007, 11:20 AM
    NorthernHeat
    2 Attachment(s)
    Gas valves



    Back to top

    If my answer helped, please click Rate this Answer! Below. Thanks!
  • Jan 29, 2007, 11:24 AM
    NorthernHeat
    1 Attachment(s)
    Heat exchanger



    Back to top

    If my answer helped, please click Rate this Answer! Below. Thanks!
  • Jan 29, 2007, 11:58 AM
    NorthernHeat
    1 Attachment(s)
    Electronic thermostat wiring



    Back to top

    If my answer helped, please click Rate this Answer! Below. Thanks!
  • Jan 29, 2007, 12:30 PM
    NorthernHeat
    Is my furnace overheating?

    Furnaces contain overheating protection by means of a limit or main limit.
    Typical symptoms are...
    • Burner turns off before thermostat temperature is reached.
    • Burners ignite again in only a few minutes after they went out.
    • Diagnostic light says main limit open.
    • Furnace keeps turning off and on when thermostat still should be calling for heat.


    To correct this problem be sure...
    • Filters are clean
    • Blower motor is running at correct speed
    • Secondary heat exchanger is clean.
    • Cooling evaporator coil is clean.
    • Cold air returns and registers are open.




    Back to top

    If my answer helped, please click Rate this Answer! Below. Thanks!
  • Jan 29, 2007, 12:49 PM
    NorthernHeat
    Roll out limit.
    This is just one example of many. However, all roll out limits must be manually reset.

    Purpose: Safety device.

    These limits trip if flames ever roll out of the heat exchanger, or flames burn where they are not supposed to be.

    If a roll out trips the potential of having a major problem with the burners are high and a service tech should probably be called to diagnose the problem.



    Back to top

    If my answer helped, please click Rate this Answer! Below. Thanks!
  • Jan 29, 2007, 01:06 PM
    NorthernHeat
    There is a button on the outside unit...Why do I have to keep pushing it?

    This button is called a high pressure cut out. It trips when the indoor airflow is poor.
    See "Why is my furnace overheating for solutions to this problem"



    Back to top

    If my answer helped, please click Rate this Answer! Below. Thanks!
  • Jan 29, 2007, 01:40 PM
    NorthernHeat
    1 Attachment(s)
    In line fuse holder



    Back to top

    If my answer helped, please click Rate this Answer! Below. Thanks!