  • Apr 30, 2009, 06:14 AM
    ballbrat1622
    Trane outside unit not kicking on
    I have an outside A/C unit that does not do anything, I replaced the thermostat over the winter, the heat kicks on with the furnace no problem, but at the thermostat you hear the click when setting the temperature below room temperature, but nothing happens out at the outside unit. I checked the ohms at the capacitor, they went from a high # to virtually 0, could it be the run/start capacitor?

    So Help me get this fixed...
  • Apr 30, 2009, 11:59 AM
    Joshdta

    Do you have 24 volts and 220 volts at the contactor? Is the capasitor swollen at the top?
  • Apr 30, 2009, 12:19 PM
    ballbrat1622
    I did not check the voltage there, but it had the voltage there before, so I would assume nothing has changed. There seems to be NO swelling with the Capacitor.
  • Apr 30, 2009, 12:23 PM
    Joshdta

    Is the contactor pulled in? If not try pushing it with a screw driver and see if it comes on.


    http://rocky.digikey.com/weblib/Pott...42D22P1-24.jpg

    Press the botton in the middle.
  • Apr 30, 2009, 12:24 PM
    Joshdta
    When you replaced the t-stat did you put a jumper from rc to rc?
  • Apr 30, 2009, 12:29 PM
    ballbrat1622
    I rewired it the same way it was wired, they are both electronic T-stats, nothing changed at all. I hear the click in the T-Stat when putting the temp below room temp.

    I will have to test the Contactor, I was not aware of this being an issue and I will check the voltage at the terminals, which ones should I test across?
  • Apr 30, 2009, 12:36 PM
    Joshdta

    Well usually the main 220 power comes to the bottom 2 termanals, ck for 220 volts at the bottom 2 and the top two. Then the 24 volts should be two small blue wires on the left and 1 on the right side of the contactor. Chack for 24 vollts between them two.
  • Apr 30, 2009, 12:37 PM
    Joshdta
    Does your indoor blower run when the t-stat clicks for ac?
  • Apr 30, 2009, 12:40 PM
    ballbrat1622
    No inside blower doesn't do anything for A/C, it works great for Furnace and the heat.
  • Apr 30, 2009, 12:41 PM
    Joshdta

    OK then is sounds like it is a t-stat problem then. If neither the indoor or out work.
  • Apr 30, 2009, 12:41 PM
    Joshdta
    Take the stat off the wall and jumper between red and yellow and see if anything comes on.
  • Apr 30, 2009, 12:42 PM
    Joshdta
    Also look for that jumper between rh and rc. Make sure it is there.
  • May 1, 2009, 08:09 AM
    ballbrat1622
    OK, I guess I am very confused as it works to kick the furnace (blower) on, it also "clicks" when the unit is on cool and you set the temp below room temp?
  • May 1, 2009, 08:16 AM
    ballbrat1622

    One thing I am confused on, again I rewired it the same way (5 wire) it was before, of course it had no issues other than the heat wasn't working before. There was no "jumper" wire then, so why would I need one now?
  • May 1, 2009, 09:24 AM
    Joshdta

    May be you old t-stst did not have a rh and a rc just a r. rh gives the heat power and rc gives the ac power. If you have the red on rh only the ac will not recive any power inless it is jumpered to rh. Same as if you only hook the red wire to rc the furnace would not get power.
  • May 1, 2009, 05:51 PM
    ballbrat1622
    I was able to check the contactor and the button was not pushed in, however when I pushed it in the outside fan came on, so it has power to the unit, I could not get any readings at the Capacitor, so what do you think?
  • May 1, 2009, 07:14 PM
    Joshdta

    Did you check to see if you had a wire on rc?
  • May 2, 2009, 05:54 AM
    ballbrat1622
    No I was not able to go inside the home at the time, I will do that, however my question would come as to how there would be power to the fan/compressor and when I hit the contactor it fires the fan up. Wouldn't that indicate there is power to the system at some point, but the capacitor is not kicking the contactor on? Or maybe the contactor isn't working as it didn't push in when the signal is sent from the inside unit?

    Just asking
  • May 2, 2009, 07:10 AM
    Joshdta

    The contactor is supposed to be pulled in by the t-stat. by you pressing it in shows that there is 220 volts going to the unit, but not 24 volts. So the problem would be at the t-stst or the indoor unit not sending the power.
  • May 2, 2009, 07:14 AM
    ballbrat1622
    OK Thanks for the information, I will check the Jumper wire and if it isn't there will replace it with one. Afterwhich I will test the system and see if it will in fact kick on or not.

    BTW, thanks for all the help and explanation.
  • May 2, 2009, 07:17 AM
    Joshdta

    No probem, if it has a jumper wire. Anouther thing you can do while you have the t-stat off the wall is to jump from r to y and see if it runs this will tell you if it is still a t-stat problem or if it is some where else.
  • May 9, 2009, 11:47 AM
    ballbrat1622

    Ok, I did go to see if it had the jumper, it did not, so I placed a jumper in, still nothing out at the unit. I can push the contactor in and the fan outside will kick on. I forgot to check about the R-Y and seeing if the unit would run, what other T-stat checks can be done. There is resistance at the capacitor and voltage at the contactor.
  • May 9, 2009, 12:09 PM
    oatmail
    Quote:

    Originally Posted by Joshdta View Post
    ok then is sounds like it is a t-stat problem then. if neither the indoor or out work.

    I totally agree here. I just want to add that the jumper he is talking about is from Rh to Rc, a typo I'm sure. This is very common with stat replacements.
  • May 9, 2009, 12:48 PM
    mygirlsdad77

    As stated in above posts, your problem is not at the outdoor unit. Forget about the outdoor unit for now. The problem occurred when new stat was installed. Double check to make sure there is a jumper between rh, and rc. Then if this doesn't work, do the rh to why jump and see if indoor blower comes on. This is most important at this point. Don't worry about the outdoor unit for now. Do your test and see if indoor blower comes on, if it doesn't come on, then neither will the outdoor unit. IF jumping rh to why at stat doesn't work, then go to the inside unit and jump are to why at the control board on furnace, let us know what you find and we will help you get this thing licked. Good luck and hope to hear from you soon.
  • May 9, 2009, 01:46 PM
    KC13
    Why do so many D.I.Y. thermostat replacements go wrong? :confused:
  • May 11, 2009, 11:08 AM
    ballbrat1622
    Ok sounds good, I will check, the problem I have it that the furnace worked for 4 months since I changed the T-Stat. However once I put the jumper wire in, the furnace didn't kick on either?
  • May 11, 2009, 03:24 PM
    mygirlsdad77

    Does anything work on the furnace now? May have blown a 3amp fuse. Its just hard sometimes for us to help fix a problem when we can't see the things you are doing. Just do one thing at a time and let us know. Start by jumping r to y at furnace control board. Also let us know if blower on furnace kicks on when thermostat is set to fan on.
  • May 11, 2009, 03:55 PM
    Joshdta

    Did you turn the power off while installing the jumper??
  • May 14, 2009, 10:57 AM
    ballbrat1622
    I did NOT turn the power off as it was simply adding a jumper, did I possibly fry the circuit board or something to that T-Stat? Because the Furnace had worked before.
  • May 14, 2009, 04:50 PM
    Joshdta

    Check the contol board for a small 3 amp car type fuse
  • May 17, 2009, 05:35 PM
    ballbrat1622
    OK, where might that control board be located? On or near the furnace?
  • May 17, 2009, 07:22 PM
    Joshdta

    Bottom door of the furnace.
  • May 20, 2009, 07:28 PM
    ballbrat1622
    1 Attachment(s)
    OK, Replaced T-Stat, looked for the fuse on the Circuit board and could not find one? The unit is a Trane TUE060A936K3.

    HELP!

    Nothing kicks on, you can hear the T-Stat Click to activate either one and nothing.

    Before installing the jumper wire the Furnace worked, after nothing works (did not shut power off when installing jumper wire, of course there were sparks) all circuits in main circuit breaker are on and good.
  • May 23, 2009, 07:18 AM
    KC13
    If the power supply to the furnace has been on for some time, the transformer should feel warm to the touch. Turn power off before checking. If it's cool, uh-oh... something is wired wrong or shorted and burned the transformer.
  • May 23, 2009, 10:40 AM
    ballbrat1622
    Ok, and this transformer you speak of is there on the circuit board? I take it this particular circuit board does not consist of the "automotive" style fuse that can easily be replaced, it will most likely need a new Control Board, right?
  • May 23, 2009, 11:55 AM
    okotoks_metis

    Manual:
    http://www.trane.com/webcache/un/spl...n_01011999.pdf
  • May 23, 2009, 01:52 PM
    ballbrat1622
    OK, with this manual you have provided, what am I looking for in these? I mean it has schematics and such, but really isn't leading me into the whole solution realm.
  • May 24, 2009, 07:10 AM
    KC13
    If you're not getting it yet, it may be time to call in a pro.
  • May 24, 2009, 08:39 AM
    ballbrat1622

    Yes it could be, however I have only done what has been suggested. I installed the JUmper wire, when I did that I failed to shut the power off, so I might have either fried the Control board since I can't seem to locate a "quick" change fuse, I am supposing I will need to change the whole control board?
  • May 24, 2009, 09:41 PM
    KC13
    Well, maybe now you are getting it. "Supposing" as opposed to effective troubleshooting usually results in unnecessary parts changing to solve a problem. It's not likely that you "fried a board", but on-site diagnostics will almost always be more effective than internet help. Did you try my earlier suggestion (checking the transformer for warmth)?