-   -   Installed new thermostat, now a/c outside unit will not run (https://www.askmehelpdesk.com/showthread.php?t=345996)

  • Apr 25, 2009, 03:06 PM
    eliz310
    Installed new thermostat, now a/c outside unit will not run
    We installed a Honeywell RTH6400 thermostat in January. We now need a/c & outside unit will not come on, inside unit runs. When we installed this we thought everything was hooked up right, but who knows. We've pulled the cover off the thermostat & we have a blue wire that is taped, should it be hooked up to something? Is this a different issue all together?
  • Apr 25, 2009, 03:16 PM
    Joshdta

    Do you have a jumper wire between rh and rc?
  • Apr 25, 2009, 03:18 PM
    eliz310

    Metal jumper wire is connected to R & Rc.
  • Apr 25, 2009, 03:19 PM
    Joshdta

    Do you have a volt meter?
  • Apr 25, 2009, 03:20 PM
    eliz310

    No, My father does, but not here. I just looked & the red wire is on Rc. Is this correct?
  • Apr 25, 2009, 03:23 PM
    Joshdta

    Yes as long as it has a jumper. Set the t-stat so the ac should come one. Then go outside and take the 2 screws holding the panel to the electric on the ac. Right where the power goes in. look for this contactor.

    http://yueqing-shi-shinaidi-electric...ges/283101.jpg

    See if the two bottons in the middle are pushed in.
  • Apr 25, 2009, 03:25 PM
    Joshdta

    Did you check the breaker to the outdoor unit?
  • Apr 25, 2009, 03:25 PM
    eliz310

    Checking will be right back.
  • Apr 25, 2009, 03:26 PM
    Joshdta

    Rember that is 220 volts so be careful you can push those buttons with a screw driver.
  • Apr 25, 2009, 03:27 PM
    eliz310
    Not finding where the power goes in.
  • Apr 25, 2009, 03:29 PM
    eliz310

    We reset breaker to unit earlier & no success.
  • Apr 25, 2009, 03:30 PM
    Joshdta

    Should be on the back left or the back right of the unit closest to the house.
  • Apr 25, 2009, 03:31 PM
    eliz310

    Already tried resetting the breaker..
  • Apr 25, 2009, 03:32 PM
    eliz310

    Is it a the entire back of the unit?
  • Apr 25, 2009, 03:39 PM
    Joshdta

    Not sure, what brand do you have?
  • Apr 25, 2009, 03:40 PM
    eliz310

    Lennox
  • Apr 25, 2009, 03:42 PM
    Joshdta

    Yes some lennox and trane units you have to take the entire pannel off.
  • Apr 25, 2009, 03:43 PM
    eliz310

    Ok, will do
  • Apr 25, 2009, 04:03 PM
    eliz310

    There is only 1 black button & it seems to be pushed in
  • Apr 25, 2009, 04:05 PM
    Joshdta

    OK if it is pushed in then your t-stat is working corectly. Your problem is with your main power. 220 volt. Is there a outside disconnect for the main power on your house?
  • Apr 25, 2009, 04:06 PM
    Joshdta
    http://www.homeairdirect.com/store/i...disconnect.jpg
  • Apr 25, 2009, 04:11 PM
    eliz310

    My husband says that if he pushed the button in, the outside fan works, but if he takes the screw driver off, then it goes off.
  • Apr 25, 2009, 04:12 PM
    Joshdta

    OK then the problem is with the t-stat wires.
  • Apr 25, 2009, 04:13 PM
    Joshdta
    See if he can find where they go into the unit. They will be buged together with the two small wires that go up to each side of the contactor, usually blue
  • Apr 25, 2009, 04:14 PM
    eliz310

    Any idea what we should do? I have a blue wire that is not connected to anything.
  • Apr 25, 2009, 04:15 PM
    eliz310
    Blue wire on the thermostat isn't hooked up to anything.
  • Apr 25, 2009, 04:17 PM
    Joshdta

    Sorry I confused you. I did not mean at the t-stat. there should be 1 t-stat wire outside and it should have a red and a white in it and out there is where they should be buged to the two blues. Make sure that connection is good.
  • Apr 25, 2009, 04:26 PM
    eliz310

    Everything seems to be connected OK outside
  • Apr 25, 2009, 04:28 PM
    Joshdta

    OK then there should be no problem there. Take your stat back off and with a jumper wire or a pair of needle nose pliers touch between
    r-y and see if the ac comes on.
  • Apr 25, 2009, 04:30 PM
    eliz310

    Outside? Sorry trying to relay message to my husband
  • Apr 25, 2009, 04:32 PM
    Joshdta

    No in at the t-stat
  • Apr 25, 2009, 04:32 PM
    Joshdta
    Take it back off the wall and jump between r and y