  • Dec 1, 2008, 04:03 PM
    Etaz
    120vac to 24 vac HVAC step down solution
    First, a brief description of my dilemma. In an effort to reduce heating/electric bills (going green!), I am in the process of replacing two mechanical line voltage fan coil thermostats in my condo with digital programmable thermostats. The building was built in the 70’s so the heating/cooling is hydronic (I think, after doing research) with a 2-pipe system. In April, the hot water starts flowing through the pipes and causes the switch connected to the pipe to switch the thermostat to “COOL” mode and vice versa. Many hours of research produced the major obstacle of finding a programmable, line voltage (120 vac) thermostat that wouldn’t break the bank. I have found (obvious to you, I am sure) that Home Depot, Menards, Sears, etc do not stock these. So I turned to the Internet and contractor supply channels. After finding one that fits all criteria and ordering, it is on back order and won’t be shipping for over a month. In addition, they weren’t cheap :-/. Ugh.

    So, instead of trying to find a digital, programmable thermostat that can handle an input of 120vac, I instead want to place a 120vac to 24 vac step down transformer (where a “normal” HVAC system takes care of this) in between the house line voltage and a 24 vac thermostat. My thinking is this would afford me a much wider array of consumer programmable thermostats that I could purchase from the aforementioned retailers. I would expect these transformers would be inexpensive and found something on Radioshack.com that does this.

    Question: Am I on the right track and if so, what kind of product would I be looking for and where would I find it?

    Thanks a ton and I look forward to your response.

    JP
    Chicago, IL
  • Dec 1, 2008, 05:42 PM
    KISS

    There is some missing info like: How many wires, what are the terminals called, what model whatchamacallits it connects too and the anticipated current at 120 it has to switch.

    Is this an auto-changeover type application? Is a fan involved? How is it controlled? Is it part of a zone controller?
  • Dec 1, 2008, 07:16 PM
    Missouri Bound
    You are on the right track, it's a very common way of solving line voltage switching... BUT as KISS said, you need to supply much more information before any of us can help you. WE're waiting.
  • Dec 1, 2008, 08:31 PM
    letmetellu

    I think you are going to have to have a relay that is operated by the 120 volts to send line voltage to a transformer that will then send 24 volts to the thermostat, so that as it makes or breaks it will send the 24 back to the really to then switch the 120 volts telling it to open or to close the water valve.
  • Dec 2, 2008, 02:38 PM
    Etaz
    Quote:

    Originally Posted by KeepItSimpleStupid View Post
    There is some missing info like: How many wires, what are the terminals called, what model whatchamacallits it connects too and the anticipated current at 120 it has to switch.

    Is this an auto-changeover type application? Is a fan involved? How is it controlled? Is it part of a zone controller?

    Thermostat(7): International Environmental TC126
    7 wires total. 3 from fan (blower)Red(HI),Blue(MED),Black(LO). 3 from sensor attached to water pipe Yellow(? ),Light Blue(COOL), Red(HEAT). 1 from hot house
    line(14GA),Brown(COM).

    Fan Coil(4): International Environemntal 4PMOD3-2 (3 speed)
    4 wires. Blue(MED), Red(HI), White(Neutral bus house line 14GA), Black(LO)

    Wires from House line(2):
    1 Black (HOT) to thermostat. 1 W (neutral) to fan White

    Now, in terms of the terminals, there is no wording at all, this is an old mechanical thermostat with just soddered connections. I made the table below to orient the connections.

    9pin connector (house side-->thermostat)
    Color Function Connects to:
    ---------------------------------------------------------------------------
    Black 120 V AC Thermost Brown(COM)
    Red (pipe sensor) ?? Switches heat/cool Thermostat Yellow
    Black Fan Hi Thermostat Blue
    Blue Fan Med Thermostat Black
    Red Fan Low Thermostat Red
    Black (pipe sensor) Heat Thermostat Red
    Blue (pipe sensor) Cool Thermostat Light Blue
    N/C
    N/C

    The house White (Neutral) connects to the fan White directly bypassing
    The above mess.

    It is auto changeover in the respective seasons. When the bldg maintence staff switches from boiler to chiller (vice versa) the sensor on the water pipe communicates to the thermostat switching to HEAT or COOL. (at least this is how I see it happening)

    The water pipes feed into a series of "fins" that cools/heats the return air. I can't see well enough to determine the mechanism of how air is returned but there is a filter we replace that sits in front of the "fins".


    Hope this helps. Thanks for your expert opinions.
  • Dec 2, 2008, 03:13 PM
    KISS

    Is there any way you can confirm what the 3 wire sensor is.

    Based on 3 wires, it's probably an RTD
    2 wires will read zero
    And between any one of these and the other; guess around 100 ohms.

    What is the typical loop temp for heating and cooling?
  • Dec 2, 2008, 03:20 PM
    KISS
    Your thinking that the fan speed is the stage and the sensor determines heat or cool based on loop temperature?

    So, I'd like to know the loop temp in heat and cooling modes?

    Some systems are Heat pump based and the loop temp isn't that much different. Your thinking that it's just a fan coil with the loop temp determining heat or cool mode?
  • Dec 2, 2008, 03:29 PM
    Etaz

    I will have to track down a maint staffer to answer the loop temp. I'll get back asap. Would a pic of the archaic system help? Being able to visualize always helps me. Not sure if I can attach low-res pics on this site since I am a newbie.
  • Dec 2, 2008, 03:39 PM
    KISS
    Their website is IEC International Environmental > Home but it looks like they are not too helpful. In their stat literature they do mention a changeover sensor, which matches what you suggested. It may measure temperature or could be an SPDT switch.

    3 heat/3cool stats might be difficult to find although you can only use 2 cool.

    You can wire a stat like you would for a damper, so it does auto changeover (Y and W are combined), so heat and cool activate the same fan speed. Then you will have to do something with G.

    Which means you won't have choice of fan speed using "FAN".

    Or you can buy their programmable stat?
  • Dec 2, 2008, 03:45 PM
    KISS

    Pics can be attached in the "go advanced" section. The limits are specified. IrfanView - Official Homepage - one of the most popular viewers worldwide resizes images.

    Any thought about going communicating stats? I'm not sure what's available.
  • Dec 2, 2008, 04:05 PM
    Etaz
    Loop temps are 42-48 and 120-140 respectively. The maint staff called it the Water FLow Sensor, which indeed does measure temp but HOW it works is beyond the scope of my objective, what it does is paramount.

    I assumed I would lose the fan speed option but who cares. Now, back to the question... can I use a transformer in my scenario so I can open up the range of programmable stats I can purchase? (i.e. install a 110-120v receptacle and plug-in a 24vac transformer and connect it's leads to the C terminal?
  • Dec 2, 2008, 04:10 PM
    Etaz
    If by two-way communcation between the stats is what you mean then, originally, communicating stats were considered but budget and simplicity overrode that option. If you meant something completely different than please fill me in.
  • Dec 2, 2008, 04:45 PM
    KISS
    It's probably out of budget: Aprilaire Communicating Thermostats &#124 HVAC Home Automation System Thermostats
  • Dec 3, 2008, 06:32 PM
    Etaz
    Quote:

    Originally Posted by Missouri Bound View Post
    You are on the right track, it's a very common way of solving line voltage switching.....BUT as KISS said, you need to supply much more information before any of us can help you. WE're waiting.

    MB or KISS,

    Do you have enough information to render further assistance? You state it is a very common way of solving the line voltage issue but I am still seeking a feasible, practical solution to my obstacle. Thanks in advance for your help.

    JP
  • Dec 3, 2008, 06:54 PM
    Missouri Bound
    Is this heating system just for your (personal) condo? Is the system actually 30 years old? In order to keep the original line voltage controls, you will need a relay to independently switch each line voltage circuit. These relays would need to be a low voltage type (typ 24ac) and they would need their own power supply and control transformer. Then a low voltage thermostat would in actuality control the relays which in return would control the line voltage load. What you have is two systems (correct me if I am wrong) that are currently controlled by one thermostat for each zone. There isn't a simple way to fix this... other than replacing the HVAC equipment. But it can be done, probably not simply or economically. You need to design a low voltage control panel to switch the line loads. You won't find one at Menards. (where are you that there is a Menards available?) You just me better off pursuing a live voltage programmable thermostat.
  • Dec 3, 2008, 07:42 PM
    KISS

    Assuming it switches a low current 120 V, these relays would be fine: https://www.ecomfrontier.com/asi/mem...on=Y&cid=11981

    They are about $10 ea. You'll need a piece of T35 DIN rail cut in two and 4 end stops. The WEB data says 24 VDC coils, but the PDF says AC/DC coils. This is about as cheap as your going to get. 3 relays, one for each speed.

    I guess the option of fan only for circulation makes no sense? Help me here.

    It's going to cost you about $40-50 just to convert the signals from 24 VAC to relays assuming two places.
    You can use two transformers or one. 1 location or two. Use DIN terminals to engineer a solution. You can put it in a box or not. All will drive up cost, but increase reliability in the long run. You can get 24 VAC DIN rail mountable power supplies.

    This diagram might clear things up a bit: http://www.white-rodgers.com/wrdhom/.../0037-6808.pdf

    You could supply power to Rc or Rh depending on the season to avoid blasts of the wrong air. You could also measure the temp of the line and switch to cool or heat mode by applying power to Rc or Rh, but that may not be the only way.

    You'll need at least a 3 heat/2 cool stat.

    See: Thermostat signals and wiring - Transwiki

    1st stageheating, will connect to low fan speed
    1st stage cooling to med fan speed 24 VAC relay coil
    2nd stage heating to med fan speed 24 vac relay coil
    2nd stage cooling to hi fan speed coil
    3 rd stage heating to hi fan speed

    It doesn't really matter if the tstat is set to electric or conventional because your not able to control the fan separately and you won't use the G terminal.
  • Dec 3, 2008, 07:54 PM
    KISS
    MB:
    A line stat doesn't come close either.

    The speed of the fan is the stage.

    I did point out that the manufacturer has programmable fan coil stats, but lacks useful online information.
  • Dec 3, 2008, 10:21 PM
    KISS

    Here is a fan coil stat:

    http://cgproducts.johnsoncontrols.co...df/2497150.pdf

    It controls the line voltage directly for the fan speeds.

    Just means the price went up:

    SC-E03-24VAC Products

    Might work?

    Don't know if you can mechanically interlock 3 relays for each fan speed. You can probably do it electrically with the aux contacts. Mechanically is safer.
  • Dec 3, 2008, 11:37 PM
    KISS

    The cool and heat wires could be used to switch the mode of the stat. Basically pick one. Make heat the failsafe position.
    Use the existing stat (you can move it out of sight) and it's sensor to determine heat or cool mode.

    I'm still assuming that there is no FAN only mode.
  • Dec 4, 2008, 12:03 AM
    KISS

    If you take a look here: Honeywell VisionPro Thermostats - iaqsource.com

    There are a number of stats. What's interesting is that Honeywell offers a gizmo that will provide and interlock the 120 control relays and, I think, provide the 24 VAC to their FAN coil stat.

    This fan coil stat does offer an speed control.
  • Dec 4, 2008, 05:06 PM
    Etaz
    Quote:

    Originally Posted by KeepItSimpleStupid View Post
    If you take a look here: Honeywell VisionPro Thermostats - iaqsource.com

    There are a number of stats. What's interesting is that Honeywell offers a gizmo that will provide and interlock the 120 control relays and, I think, provide the 24 VAC to their FAN coil stat.

    This fan coil stat does offer an speed control.

    KISS,

    Would this model work in my application? It uses 120V AC input but I am not sure if it would work in my application. It is made by CAS.

    Model No. System Fan Function
    T202-G5B63 Heat/Off/Cool Auto/on 3 speed

    Here is the wiring diagram. I just am not sure where the pipe sesnsor connections would go.
    Wiring

    1 stage Heat / 1 stage Cool
    -------------------------------
    1- Input (L1)
    2 -Common
    3 - Heat
    4 - Cool
    5 - Lo fan
    6 - Med fan
    7 - Hi fan
    8 - Rev. Valve heat
    9 - Rev. Valve cool

    1 Heat / 1 Cool
    Heat Pump
    ------------
    Compressor, add Jumper to 3,4

    1 - Input (L1)
    2 - Common (Neutral)
    3 - Heat 1 stage
    4 - Cool 1 stage
    5 - Lo fan
    6 - Med fan
    7 - Hi fan
    8 - Rev. Valve heat (damper)
    9 - Rev. Valve cool (damper)

    Is this stat even applicable to 2-pipe heat/cool system? I am going to attach pics for you to enjoy of my lovely system. I have also attched a PDF of the CASD stat I was looking at.

    To answer MB's question, there are two independent systems in each corner of the condo. The 2-piping water source (see pic) is common piping to all units so if bldg "boiler" or "chiller" goes down then all units in bldg suffer. But thermostatic controls are per unit. A guy in a nother unit replcaed his mechanical (original IEC) t-stat with the non-programmable honeywell T6575 but I was looking for a programmable option.

    Thx.
  • Dec 4, 2008, 05:19 PM
    Etaz

    Actually, take peek at this http://www.ntsupply.com/files/products/62-0278.pdf

    I would have places to put all my wires incl. the sensor wries. Which wiring scenario would be most applicable and can I rig the T202 with this wiring in mind?
    I know... I'm all over the road but bear with me I really appreciate your time.
  • Dec 4, 2008, 05:27 PM
    Etaz

    I am still unclear on how to attach pics/files. Infraview seems to be just a freeware image viewer. Is there a site I can attach images to and just post the links in this forum?
  • Dec 4, 2008, 05:36 PM
    KISS

    Page 2 is very similar to your stat. In fact the lower link is identical.

    http://l.b5z.net/i/u/6065183/i/T202_Rev_A_6-29-05.pdf

    I may have an idea. Let me think a little bit.

    Is Heat/Cool used on the original stat? Somehow I don't think so.
    So, I think all we may have to do is prevent Heating or Cooling based on the pipe temperature. Does this seem reasonable? Now what bothers me is the contact ratings. Is it possible to read any info off the fan motor? Like HP or FLA and LRA?

    Here: http://www.ntsupply.com/files/products/62-0278.pdf

    Page #5 is interesting.
  • Dec 4, 2008, 05:37 PM
    KISS
    Pictures:

    Use "Go advanced" and then "Manage Attachments"

    Irfanview is an image resizer if it does fit the size requirements.
  • Dec 4, 2008, 05:38 PM
    KISS
    Any possibility you can get a wiring diagram of the FAN coil and get it scanned?
  • Dec 4, 2008, 08:38 PM
    KISS

    Ah. Ideas coming to life.

    http://controlsdepot.ca/siebe/pdfs/REDPDF/TC2931.PDF

    Available at:

    South Side Control Supply Co Invensys Barber Colman TC2931 Strap On Changeover Stat 75F TC-2931

    Now we are getting somewhere.
  • Dec 4, 2008, 08:48 PM
    Etaz

    Yep, that's it. But that works! I don't need another one of those. Ohhhhhh... I see you were thinking out load ;-). Is all my psycho-blabber starting to "connect"?
  • Dec 4, 2008, 09:03 PM
    KISS

    Yep. Thinking outloud.

    I need a question answered:

    Am I correct that the fan is not allowed to run to just circulate air, because if it did it would blow hot or warm air, correct?

    I think I can make it work "correctly" with one contactor and 1 additional relay + the Changeover switch above.

    I need to sleep on it.
  • Dec 4, 2008, 09:10 PM
    Etaz

    You are correct. Fan has to blow whatever the temp of water is running through the pipes.
    "chat" later...
  • Dec 4, 2008, 09:22 PM
    KISS

    The "pipe sensor" is probably like the TC2931 switch and not a temperature sensor at all.
  • Dec 4, 2008, 09:32 PM
    KISS
    I think by adding the following logic, the t-stat will work.

    If (water hot) and (call for heat) Motor is allowed to run.

    If (water cold) and (call for cool) Motor is allowed to run.

    (allowed to run) means t-stat controls the speed of the motor from off to high.
  • Dec 5, 2008, 09:43 AM
    KISS

    A few comments at this point:

    To those reading, some pics were too big and sent privately.

    The possible stat CAN be made to work with some effort. I'm waiting for the mfr to reply concerning what Auto means. It can be Auto-changeover because of the pipe temp or auto-changeover because of a heat and cool setpoint.

    There may be other stats available. I didn't have a chance to look at another promising one. Now that I know what I'm looking for, it should be a bit easier.

    The changeover sensor is probably an SPDT switch and it would have to be used.

    The energy savings may not be as steep as you would think because you may only be paying for electricity to run maybe a 1/3 HP motor. Maybe 300 W when running.

    The changes required, which I would like to avoid, in words would be:

    A junction box or enclosure would have to be put in the FAN COIL enclosure to protect the suggested additional controls.

    HEAT and COOL wires would have to be used in the tstat box. You probably can use 2 of the 3 wires from the changeover sensor that are running to the current stat.

    A contactor would have to be placed on the Neutral side of the motor. (Motor allowed to run). [Need nameplate data to size]

    A DPDT relay (120 V coil) would also be used. It would be designed such that when OFF, heat is the default mode. The Changeover sensor (2 of the 3 wires) will be used to provide the switch to energize this coil when the loop water is hot.

    What this relay will do is select the HEAT or COOL output of the stat and power the coil of the added contactor. If chatter occurs a small time delay relay can be added.

    Standard DIN rail construction techniques can be used. Bushings would have to be used for the penetrating wires.
    I'm not real happy about the wire nutted motor connections not in a junction box.

    So, in theory, it's possible.
  • Dec 5, 2008, 12:00 PM
    KISS

    This was a Carrier stat I found http://www.docs.hvacpartners.com/idc.../33cs-56si.pdf

    But there is one major gotcha. The fan has to run on Low all the time unless off.

    It's a low voltage stat and a relay interface board is required.

    The necessity of the fan running all the time makes this one impossible to use
  • Dec 5, 2008, 02:02 PM
    Etaz

    All this EE talk of throwing new relays and contactors into the witch's brew is making my headspin. Let's step back and scale back.

    What if I lose the ability to auto-changeover<grimace>, make it a manual step from the stat. Cap off the sensor wires. Now what do we have? Given the T202 stat that I would like to work in the existing framework, what would have to happen. Refer back to the wiring diagram earlier. Having 3 speeds on fan is overkill, so only have LO or MED speed available when energized? My head is still spinning. :-|
  • Dec 5, 2008, 02:08 PM
    hvac1000
    Actually a 3 speed manual selector switch for 8.00 bucks on Ebay does the trick. Got one on my unit a camp. When playing cards with the guys I just dial it down to the next lower speed. Nice and quiet. I just bolted it to the furnace in a 4x4 handy box.
  • Dec 5, 2008, 02:12 PM
    Etaz
    Addendum. Let me reflect on my original obective: Replace archaic manual stat with programmable digital stat for energy savings and more presice temp control.

    Now I have walked into a realm where I should just boil water over a flame and watch the hamster on the wheel chase the Cheezit to run the gernerator to power my girlfriend's hair dryer.
    Your screenname says it all, KeepItSimpleStupid. Let's hover over this acronym and apply it here. Or because of the archaic system, in order to achieve long term energy savings do I HAVE to throw money at the solution up front? Re-engineering cost savings is also paramount due to budgetary constraints.
    Fire when ready... :-/
  • Dec 5, 2008, 03:09 PM
    Missouri Bound
    Etaz... would you consider moving? Seems like a lot less of a headache. And somehow the phrase "keep it simple stupid" doesn't apply to this anymore. Hmm... Well thanks for opening up the doors Etaz, once in a while it's nice to have our interest peaked. As I said early on you are on the right track. But it would behoove you to have someone you personally know and trust look at the system and advise you rather than make any changes based on comments made on this informative but alas long distance information forum.

    Keep the faith.
  • Dec 5, 2008, 03:28 PM
    Etaz

    Don't blame you a bit, MB. Thanks for your input. It has been enlightening and I will pursue the suggestions rendered in this forum. Cheers.
    Nowwww where did I put my analog TV antenna...
  • Dec 5, 2008, 03:56 PM
    hvac1000
    1 Attachment(s)
    Quote:

    Originally Posted by Etaz View Post
    Don't blame ya a bit, MB. Thanks for your input. It has been enlightening and I will pursue the suggestions rendered in this forum. Cheers.
    Nowwww where did I put my analog TV antenna...


    Here is part of your system. It was built for a prison but something like this will work for you. Now all you have to do is figure it all out.